Hi All,
I have a problem with a Mitsubishi FX2n PLC, the system is set up and has been operating for over 10 years in the following configuration.
SCADA (MX32) comms via RS232 to two FX2n PLC's using a FX2n-485-BD card to effect communications, the station numbers are 0 and 1, and the communications bits are:
Hex: H6097
Binary: 0110 0000 1001 0111
Station 0 is an FX2N-64MR, interrogation of this station using GX Developer shows a communications error 'PLC/PP Comm error' further investigation shows M8062 set to 1 (Error Present) and the value of D8062 is 6201.
All cabling has been checked and is without fault
I have replaced the FX2N-485-BD card on both stations as part of the fault finding routine
The SCADA system has intermittant communication with station 1 but no communication with station 0
Soft and hard reset of the complete system has been tried, the fault on station 0 will not clear. The fault appears to have occured during a period of electrical storm activity, and I am no looking at replacing the PLC as that is the only part left.
Any advise or wise words would be appreciated
Thanks in advance
Mark Bolton
I have a problem with a Mitsubishi FX2n PLC, the system is set up and has been operating for over 10 years in the following configuration.
SCADA (MX32) comms via RS232 to two FX2n PLC's using a FX2n-485-BD card to effect communications, the station numbers are 0 and 1, and the communications bits are:
Hex: H6097
Binary: 0110 0000 1001 0111
Station 0 is an FX2N-64MR, interrogation of this station using GX Developer shows a communications error 'PLC/PP Comm error' further investigation shows M8062 set to 1 (Error Present) and the value of D8062 is 6201.
All cabling has been checked and is without fault
I have replaced the FX2N-485-BD card on both stations as part of the fault finding routine
The SCADA system has intermittant communication with station 1 but no communication with station 0
Soft and hard reset of the complete system has been tried, the fault on station 0 will not clear. The fault appears to have occured during a period of electrical storm activity, and I am no looking at replacing the PLC as that is the only part left.
Any advise or wise words would be appreciated
Thanks in advance
Mark Bolton