We are an oem and have never used the GE 9030 with remote i/o racks, our firs attemp has failed miserable with our racks faulting. The tech support at GE seem to think we have everything set up right but still can not communicate with the remote racks.
we have the IC693BEM331 modual in the 5th slot.
Any help or suggestions would be greatly appreciated.

Thank you

bryan
 
I would be happy to take a look at it also. Usually the problem lies with a mismatch in the amount of data being passed to and from the CPU.

Which remote racks are you using? Versamax? Are there any entries in the PLC and I/O Fault tables?

The more data you give, the more we can help.
 
If the configuration is correct:
1. Make sure that you have the proper cabling.
1a. Proper termination, based on your cable spec.
1b. NO SPLICES!
1c. The SAME cabling spec. throughout the network.
2. Proper wiring.
2a. Shield-IN to Shield-OUT *DOUBLE* check this!
3. Proper cable routing.
 
Thank you for your replies: the problem was that the rack addresses didn’t start at zero for the different card types. After the input card was given a length of 16 the output card was then started at 17. All card types needed to start at zero. This error was a throw back to the AB days. All is well now and thanks again for your replies.

 

Similar Topics

Hello Everybody Iam first time using Gefanuc Genius IO Module , so i want to list out the hardware it requred for communication to PLC.We are...
Replies
5
Views
3,625
Hello, i am using profibus as communication between plc and fanuc arm. I can easily send inputs from plc to arm, but i can't monitor any outputs...
Replies
0
Views
68
I have a CNC cutting equipment, all the components are Fanuc from the CNC CPU A02B-0307-B822, a PLC AIF01A and a panel i, on the panel i (operator...
Replies
1
Views
145
I want to buy this program if anyone has it. Absolutely no one has it officially for sale. My cpu is IC610CPU104B My mail...
Replies
2
Views
134
I've got a Micrologix 1100 with ethernet and I'm trying to configure communications to a Fanuc R30iB controller. I'm pretty sure you have to set...
Replies
0
Views
126
Back
Top Bottom