Hello,

I replaced an old S5-135 and four IM308 with a 315-2 PN/DP and four CP342-5. On each Profibus there are S7-300 and S5-95U slaves.
Now I have a little problem... the communication processor on one of these s5-95U slaves may fall down but CPU continues to run. So I have to switch off or reset the slave to relaunch the communication processor. What's going wrong ? (all the hardware has been renewed and checked).
 
I find your description a little confusing.

If one entire Profibus network is not working, you have to reset one of the attached slaves to get comms to all slaves up and running ?
That sounds odd.
If all slaves on one CP is not communicating, you can try to investigate the Hardware Diagnostics on the 315.

Or is that if one slave on one of the networks is not working, you have to reset that slave to get it up and running ?
That sounds logical.
If the affected slave is an S7-300 setup as intelligent slave, then look into the diagnostics buffer of that PLC.
Cant help you with S5-95U. Seriously you should plan for exchanging these with something newer.

Maybe you can try to program automatic disable and enable of the affected slaves. You use SFC12 for this.

How many DP slaves are there ? I just find it odd to install that many CP342-5's. All data still have to pass through the same backplane on the 315.
Maybe a single 317-2DP would have been a better choice, with each of the two available ports on the CPU handling one Profibus network.
 
It's only one s5-95U on one of the 3 networks that's falling down and it's not always the same...

Network 1: 1xS7-300DP; 8xS5-95U-DP.
Network 2: 7xS7-300DP; 2xS5-95U-DP.
Network 3: 1xS7-300DP; 2xS5-95U-DP.
Network 4: 16xS7-300DP.

The S7-315 says that this slave doesn't exist on the network...
 
Do you have some diagnostics capable adapter (like a CP5511, CP5512 or a CP5611) to see if the missing slave is present on the network ?
If it is present, you could try the SFC12 to diable/enable the affected slave.

Can you rule out noise or other problems ?
What is the busspeed ? You can try to run at 187.5k and see if that helps.
 

Similar Topics

Hi I have a question about Profibus DP communication. What blocks should I use to set up a communication between a CPU315-2DP (Slave) and a master...
Replies
3
Views
2,454
Hi there, I have a configuration like following: 1x S7-315-2DP with 1x CP342-5 Several Lenze 8200 inverters with profibus function module...
Replies
4
Views
2,555
Hi All, As a precaution my company has been collecting copies all the HMI and PLC programs. I have recorded copies of most of our sites...
Replies
0
Views
76
Dear sir, I am using SIMATIC 300, CPU 315-2DP , (6ES7 315-2AF03-0AB0) VIPA 603-1CC21 A1.0 RAM 32KB, Firmware=V4.0.8 The problem Im using MPI...
Replies
2
Views
188
Hi , Looking for some help. We have a 343-1 PN Lean Card & 315-2DP connected to an external system collecting data. After a recent shutdown...
Replies
0
Views
73
Back
Top Bottom