I am having big time trouble setting up my PLC, I am using rslogix5 to a kf2 to a 5/25 processor in a 16 slot rack. I went through the directions for setting the dip switches and think I have them set right but, I cant go on line. I am using rslinx lite 1.7 and have configured the kf2 to its proper settings using the auto configure. This is the only PLC on the DH+ so it is not getting confused with any other nodes.
I have set the processor dip switch 1 to node 00 and adapter mode, but I am not sure if switches 2 and 3 are set correct. If they are not, will this prevent me from going on line??? Switch 3 look straight forward, I have them all open(off) 1: plc terminator open for 150 ohms out
2: remote I/O terminator open for 150 ohms out
3: not used open
4: not used open
It is switch 2 that I am cofused with, right now it is set to:
1: open for full rack
2: open for baud used
3-8 closed as in the diagram on the processor for node 00
I set the chassis switches to
1: open(off) for I/O are turned off if a hardware error happens
2 & 3: always open as in diagram
4 & 5: open/closed for one slot addressing
6 & 7: open/open for EEPROM memory transfer to processor on power up
8: open for memory protection disabled
Now that the switches were set to these specs, I configured the processor and chassis in rslogix to match, but when I try to go on line, it cant find the processor....@$#%&%$
Any suggestions would be great...thanks for your time....JEFF
I have set the processor dip switch 1 to node 00 and adapter mode, but I am not sure if switches 2 and 3 are set correct. If they are not, will this prevent me from going on line??? Switch 3 look straight forward, I have them all open(off) 1: plc terminator open for 150 ohms out
2: remote I/O terminator open for 150 ohms out
3: not used open
4: not used open
It is switch 2 that I am cofused with, right now it is set to:
1: open for full rack
2: open for baud used
3-8 closed as in the diagram on the processor for node 00
I set the chassis switches to
1: open(off) for I/O are turned off if a hardware error happens
2 & 3: always open as in diagram
4 & 5: open/closed for one slot addressing
6 & 7: open/open for EEPROM memory transfer to processor on power up
8: open for memory protection disabled
Now that the switches were set to these specs, I configured the processor and chassis in rslogix to match, but when I try to go on line, it cant find the processor....@$#%&%$
Any suggestions would be great...thanks for your time....JEFF