Omron AD081-V1 Analog Input Card Calibration (Offset & Gain Adjustment)

Ko Lin

Member
Join Date
Apr 2024
Location
Singapore
Posts
1
Omron AD081-V1 Analog Input Card
Offset & Gain Adjustment

Entering Adjustment Mode

1. Set the input card in adjustment mode (Turn ON Dip SW No-1)
2. Turn ON PLC
3. Set PLC operation mode to “Program”.
4. ADJ yellow indicator will Flash while unit is in adjustment mode and PLC is in Program Mode.

Offset Adjustment.
1. Set #21 into CIO 2000 (For Unit 0, Analog Input Card Ch-1) (For Ch-5, Set #25)
2. Turn ON bit 00 of CIO n+1 (2001.00)
3. Input 4.00 mA to Channel-1
4. Monitor the conversion value in CIO n+8 (2008)
5. Thurn ON bit 04 of CIO n+1 for offset adjustment (2001.04)
6. Turn OFF bit 04 of CIO n+1 for completing offset adjustment (2001.04)
7. Turn OFF bit 00 of CIO n+1 for exiting offset adjustment (2001.00)

Gain Adjustment
1. Set #21 into CIO 2000 (For Unit 0, Analog Input Card Channe-1) (For Channel-5, Set #25).
2. Turn ON bit 01 of CIO n+1 (Which is 2001.01)
3. Input 20.00 mA to Channel-1
4. Monitor the conversion value in CIO n+8 (2008).
5. Thurn ON bit 04 of CIO n+1 for gain adjustment (2001.04).
6. Turn OFF bit 04 of CIO n+1 for completing gain adjustment (2001.04)
7. Turn OFF bit 01 of CIO n+1 for exiting offset adjustment (2001.01)

Existing Adjustment Mode (Put the Input Card to Normal Mode)
1. Turn OFF the power of PLC.
2. Set the input card to Normal Mode (Turn OFF Dip SW No-1)
3. Turn ON the power of PLC

NOTE:
2000 : Selecting Channel for Adjustment (Ch-1: #21, Ch-2: #22, …., Ch: #28)
2001.00 : Offset Adjustment
2001.01 : Gain Adjustment
2001.04 : Writing New Conversion value to EEPROM
2008 : Monitoring Conversion Value while Setting #21 into CIO 2000
 

Similar Topics

Hi all its me again!! Omron AD081 I am using an Omron ADo81 analogue input card. And i have read the manual inside out. I cannot understand the...
Replies
6
Views
6,947
Has anyone done SMS messaging from an Omron CJ2J-CPU31 PLC? If so could you help please. Omron here in Oz have not had any experience doing this...
Replies
5
Views
178
I have an old plc in the system I have, moxa nport was used to communicate with scada, I want to replace the plc with cj2m cpu33 and eliminate...
Replies
1
Views
66
Hi all, i have 8 CJ2m plc units that show different numbers on the plc display and i am stuck on reading the info. my unit has an ip address of...
Replies
3
Views
110
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
Replies
6
Views
264
Back
Top Bottom