PV+ 1500 Keypad on DH485 Questions

504bloke

Lifetime Supporting Member
Join Date
Jan 2005
Location
Down South
Posts
2,721
Hi

Couple of question about the PV+1500 with an RN6 module fitted

First the DH485 termination connector, terminal 6 states terminating resistor but i cant find anywhere that explains the use of this ??

Second the unit is Keypad only (not touch) but the mouse cursor is in the center of all screens, is there anyway to turn the mouse cursor off ??
 
The mouse can be turned off in the set up as well as many other settings.
I thought I had a link to a note that showed how the risister is used but I can't find it.
 
The mouse cursor can be enabled or disabled in the Terminal Settings -> Display -> Cursor configuration selection.

RA Knowledgebase document ID # 25503 describes this as well as the navigation for earlier firmware and VVCE terminals.

The DH-485 trunk connector on a 2711P-RN6 module works just like those on any 1747-AIC or 1761-NET-AIC. The Pin 1 "termination" terminal is connected with a 120 ohm resistor to the Data B terminal internally.

Jumpering the Data A terminal (#2) to the Termination terminal (#1) connects this resistor between Data A and Data B. Only do this on each extreme end of the daisy-chain. See the rest of the DH485 documentation for the shield drain connection.
 
Thank guys.

Ken - I am replacing an old PV1400, this is connected to a 5/04 in this fashion


5/04 - AIC+ - AIC - PV1400

Resistor at each end

So presumably i can do this

5/04 - AIC+ - PV+ ?? And use the terminals term 6 term resistor ?

Also i remember reading a previous post from you regarding the Linx Enterprise setup and having the DH+/DH485 set to comm port 2 as comm 1 is the rs232 on the terminal, is this correct and where do i find this (In FT VIEW)?

PS I did look in the terminals config but missed that one about the cursor!
 

Similar Topics

Hello all. I am working on a project where I am converting an old enhanced panelview terminal on remote IO to a panelview plus 1500 keypad. Does...
Replies
0
Views
1,757
Can we use a Simotion D455 ethernet port x127 as a gate, to access S7-1500 plc Tia Portal program ? In the Simatic manager, we used Netpro to do...
Replies
2
Views
85
I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
80
Hello, I have a 1764 1500 LSP Series A that keeps failing with DTL_E_FAIL I/O error. Searching around it seems there's a weird issue specifically...
Replies
2
Views
103
Hi all Trying to remotely connect to a TIA Portal PLC. I can ping it without a problem but can't get my software to connect. I've opened port...
Replies
8
Views
324
Back
Top Bottom