Tim Hixson
Member
I have 2 plc problems.
- I have an Encoder/Counter Module for a Allen Bradley PLC5. The module faults every once and a while (count gets too big before the zero command resets the count to zero) Is there a way to reset the fault in the status word? The only way I have been able to reset the module is to cycle power on the RIO rack it is mounted in. Any better ideaas?
- The last problem is with my DH+ network. Currently I have on the network is PLC5/15, PLC5/15, PLC5/25, SLC5/04, and Control logix PLC. If I connect my lap top to the network the network will crash. This means that I can not trouble shoot the equipment while it is running. The 1st 3 PLC's are part of the original network. We added the SLC 5/04 and the Control logix. This is when the problem started. I found "MSG" commands in the original 3 PLC's that were set up for "Continuous Run" in the Control Bits. I have not found a good explanation on what this means. I am deactivated continuous run, but the production manager is hesitant to allow me to connect to the network to see if this solved my problem. Can anyone explain "Continuous Run"?