Dear all,
Would any master please help me to solve the SLC5/05 hotstandby Remote IO system. I had connect the system as per manual stated but only my Primary SLC can run and the Secondary don't run and give error:
"Specially I/O module in slot 1 has not responsed to a command as being completed within the required time limit" and program keep on stopped by error.
I had config the system and connect as per manual with Belden 9463 cable:
1. Connection between 2 BSN HSSL
2. Connect 2 BSN at the RIO terminal and ASB with 82ohm 1/2Watt resistor add to the terminal at 1st BSN and the ASB.
however, system cannot work and on
Rack 1 BSN shows:
1. Steady Green Primary Light
2. Flashing Green RIO Light
3. Flashing Red ERR Light
4. HSSL off
Rack 2 BSN shows:
1. Primary and Secondary off
2. RIO off
3. ERR off
4. HSSL off
5. FLT Flashing Red
Remote Rack keeps on show:
1. COM Flashing Green
2. Fault Off
3. Status display ArE
My SLC system config as below:
Rack 1 (4 Slot)
SLC551
1747-BSN
Rack 2 (4 Slot)
SLC551
1747-BSN
Remote Rack (10 Slot)
1747-ASB
1746-IB32 (5 nos.)
1746-OV32 (1 no.)
1746-NI8 (2 nos.)
My 1747-BSN config as below:
Master (Rack 1)
010001 230.4K Speed, Last Module
0000 Address=1 (Slot 1)
Slave (Rack 2)
010000 230.4K Speed, All Others
0000 Address=1 (Slot 1)
My 1747-ASB config as below:
I use 1/2 slot config with speed 230.4K
11111111 (Dip SW 1)
01011001 (Dip SW 2)
11100111 (Dip SW 3)
Best Rgds.,
Man
P.S.: I had getting tired of solving the problem and would any master can give me some hints or solution. Thousand Thanks in advance for your kindly Assistance.
Would any master please help me to solve the SLC5/05 hotstandby Remote IO system. I had connect the system as per manual stated but only my Primary SLC can run and the Secondary don't run and give error:
"Specially I/O module in slot 1 has not responsed to a command as being completed within the required time limit" and program keep on stopped by error.
I had config the system and connect as per manual with Belden 9463 cable:
1. Connection between 2 BSN HSSL
2. Connect 2 BSN at the RIO terminal and ASB with 82ohm 1/2Watt resistor add to the terminal at 1st BSN and the ASB.
however, system cannot work and on
Rack 1 BSN shows:
1. Steady Green Primary Light
2. Flashing Green RIO Light
3. Flashing Red ERR Light
4. HSSL off
Rack 2 BSN shows:
1. Primary and Secondary off
2. RIO off
3. ERR off
4. HSSL off
5. FLT Flashing Red
Remote Rack keeps on show:
1. COM Flashing Green
2. Fault Off
3. Status display ArE
My SLC system config as below:
Rack 1 (4 Slot)
SLC551
1747-BSN
Rack 2 (4 Slot)
SLC551
1747-BSN
Remote Rack (10 Slot)
1747-ASB
1746-IB32 (5 nos.)
1746-OV32 (1 no.)
1746-NI8 (2 nos.)
My 1747-BSN config as below:
Master (Rack 1)
010001 230.4K Speed, Last Module
0000 Address=1 (Slot 1)
Slave (Rack 2)
010000 230.4K Speed, All Others
0000 Address=1 (Slot 1)
My 1747-ASB config as below:
I use 1/2 slot config with speed 230.4K
11111111 (Dip SW 1)
01011001 (Dip SW 2)
11100111 (Dip SW 3)
Best Rgds.,
Man
P.S.: I had getting tired of solving the problem and would any master can give me some hints or solution. Thousand Thanks in advance for your kindly Assistance.