PID Control

junkerjorg

Member
Join Date
Nov 2007
Location
Wisconsin
Posts
56
I have been given the task of programming a PID loop to control a product pump off of a pressure transmitter. This will be my first PID loop and I'm not really sure how to do this.

Would someone be willing to help me through? I would greatly appreciate it.

PLC is a PLC 5/80 - I/O is already all mapped out
4-20mA and right now I am assuming 0-4095 on the scale
Inverter is AB Powerflex 40, Speed controlled at O:037.3
Pressure xmitter I:035.5

Thanks!!
 
There are a lot of PID threads. If you look up at the top, use the search function. I however, am not a pid guru. Look for posts from guys like Peter N. or Ron B. They are very very informative. Unfortunately for me, alot is over my head. Good Luck.
 
Check out controlguru.com, I've linked you to his table of contents, start reading at section I.2 "Heat Exchanger Study" continue into the other sections and read everything that relates to the Heat Exchanger, once you've understood that, start reading each sub-section. He does a great job of teaching the fundamentals of the PID and how to go about tuning, it isn't specific to certain PLC's but a good overview of the PID concept. Once you understand the concepts turn to the PLC 5 instruction set manual for specifics on setting up the PID in the logic.
 
Greetings junkerjorg ...

sorry that I don't have much spare time right now - but if you'll post your existing .RSP file, the other forum members and I will be glad to take a look at it ... for one thing, I'm not sure what addresses you had in mind, but the ones that you listed in your first post don't seem quite right for analog signals in a PLC-5 system ...

I recommend that you let us help you nail down the addressing and the scaling before you try tuning, etc. ...
 
Ron,

I appreciate the response, I know you are a very busy man! As I stated I did manage to sort things out but here is a screen shot for you to review. I apologize for the addresses, they were the physical addresses where the components are to be wired.

Regards,
Steve

jj.JPG
 

Similar Topics

I have S7 1512C controler for controlling 48 PID temperature loop, the output is PWM. Please I need the best, most efficient way to write the...
Replies
13
Views
604
Hi all, I'm having trouble solving a problem I've been working on for several months, and thought you might like a stab at it. The machine runs...
Replies
22
Views
952
How can I connect PID Output to a valve. In ladder logic program is there any logic do I want to add between valve and PID? PV=SP What will be the...
Replies
7
Views
418
I am setting up control for Hypochlorite dosing. The easy part is the dosing calculation for flow pacing but I would also like to setup trimming...
Replies
8
Views
948
Hey guys! I'm a newbie in the control area, so I'm gonna drop some thoughts here... We want to control the opening of big silos (about 1900...
Replies
6
Views
1,490
Back
Top Bottom