Q01 CC-link

sttchui

Member
Join Date
Mar 2008
Location
kl
Posts
81
Hi

I am looking for the Mitsubishi Q01CPU setup programming manual for the CC-link.

i trying to link up the Q01CPU to 2 unit of AJ65SBTB1-16D & 2 unit of AJ65SBTB2N-16R.

Any helpful tips i is highly appreciate.

Thank you!

Regards,

sttchui
 
thanks for the link.


But i still having problem setting up the cc-link with my plc.
Does anyone have sample program to guide me to link up with my module?

CPU Q01 with IO QX41,QY41
cc-link :QJ61BT11N(starting address 40)

Remote IO: AJ65SBTB1-16D(2 unit, address 1 & 2 with baud rate 156k)

AJ65SBTB2N-16R(2 unit, address 3 & 4 with baud rate 156k)

when i switch on the power, the ERR led on the cc-link is flashing, i have double check the dip switch & wire & resistor, everything is ok but i still receive this error??

any help or suggestion are welcome.

Thank you!
 
sttchui said:
thanks for the link.


But i still having problem setting up the cc-link with my plc.
Does anyone have sample program to guide me to link up with my module?

CPU Q01 with IO QX41,QY41
cc-link :QJ61BT11N(starting address 40)

Remote IO: AJ65SBTB1-16D(2 unit, address 1 & 2 with baud rate 156k)

AJ65SBTB2N-16R(2 unit, address 3 & 4 with baud rate 156k)

when i switch on the power, the ERR led on the cc-link is flashing, i have double check the dip switch & wire & resistor, everything is ok but i still receive this error??

any help or suggestion are welcome.

Thank you!
In the CC Link config in GX DEV have you set the parameter
'All connect Count' to 4 as you have 4 cc link modules in the system.
 
Thanks alot Mike!

It work as it should now. after i change count to 4, you a great help.

Thank you & Have a nice day!
 

Similar Topics

Hi, I have just started with Mitsi PLC. Have a bare rack with only power module and a Q01. Have a new project, one test rung. After transfer I...
Replies
2
Views
3,068
I'm workning on the attached file, this is my first run in with CX Designer and I cannot find where to add/edit message screens. Can someone help...
Replies
0
Views
4,211
Good afternoon, I have a problem communicating with a system, I will explain it briefly. I have a HIS -ML17- CTBH monitor connected to an...
Replies
16
Views
444
I'm struggling to get an FR-E800SCE to work on CC-Link IE TSN. I'm sure the issue is with the drive, when I plug in the network cable I get no...
Replies
1
Views
121
Hi everybody, I would like to know if anybody here has already programmed with a LR-TB keyence on Io Link on a Rockwell PLC? And perhaps have...
Replies
0
Views
104
Back
Top Bottom