Mitsubishi Q01 Missing Parameter (beginner)

spaderkung

Member
Join Date
Aug 2007
Location
South Sweden
Posts
389
Hi,

I have just started with Mitsi PLC.

Have a bare rack with only power module and a Q01.
Have a new project, one test rung.

After transfer I get error Missing Parameter File. Otherwise ok to go online and toggle bits. But cpu is in stop.

Transfer settings has been program + parameter.

Thanks
 
Thanks,

CPU needed to be reset after download for HW changes to apply. I think the old CPU set up may have included other cards, and the missing parameter error 220 referred to that.
 