Simoreg 6RA70 Drive Field voltage to increase

mvannantn

Member
Join Date
Jan 2003
Location
bangalore
Posts
32
I wants to increase the drive field voltage from 215 to 330.Please any one help in this regards.The connected motor field voltage is 330 with 3.2/5.1 Amps. But the drive giving the out put voltage of 220 and the current is 4.7.

Regards,

Mani
 
Set the drive up for field current regulation, and set that.
Field current is more accurate, and meaningful, then voltage control, as the winding resistance changes with heat.
 