Hi to all,

Can somebody maid have any experience with ADAM remote I/O device 6024? I have recently received one system full of mistakes, and trying to solve a lot of problems on it. I need to filtrate some disturbances comming on the same input, but input itself is logical 1 for only 30 ms, same as disturbances.

I can solve this creating some rules, but ADAM 6025 does not support to configure "low to hi signal latch" mode for input in the rule. Just in remote mode I think?

If somebody has some advice I will appreciate!

Thanks to everybody!
 
Adam 6052

My rude mistake... It was ADAM 6052.

Problem is: GCL does not support all types of inputs which is possible to set in remote mode?

Unbelieveable.....
 
Please consider that the GCL is not a full language, if you want a latch you will have to wire it yourself.

Included are examples of a "High to Low" and "Low to High" wired using two NAND gates, this is derived from the basic Set/Reset NAND example everyone learns in a basic electrical engineering class.

DI0 is the Set
AuxFlag0 is the Q (or output)
AuxFlag1 is the Reset


Disclaimer: I work for the company that makes these modules.
 
Thank you for your answer and your help;

Latch - unlatch function is really essential and not a problem to make it aditionally; just, I`ve been asking DOES Adam support this function, because it supports in remote mode but not in GCL mode.

I`ve already solved this problem, latching and unlatching, applying one more ADAM in between, and sending pulse output to the GCL programmed ADAM. This is all I could do here in Kuwait, because, receiving anything from outside takes time. Nothing`s available here, unfortunately.

Thanks again!
 

Similar Topics

who can teach me how to edit tag adam 4017+ in citect scada? real external I/O
Replies
0
Views
880
After great help on the forum getting a Red Lion G3 HMI to control & communicate with Advantech's ADAM-4055 D/IO modules, the next step was to...
Replies
15
Views
4,353
Thanks to some great advice on this forum after I asked the question: Could I communicate with a remote D/IO module (Read & Write) using only a...
Replies
10
Views
3,951
Does anyone know how to get a ADAM 6217 Analog Input module talking to a Productivity 2000 PLC over Ethernet/Modbus?
Replies
3
Views
1,884
Back
Top Bottom