What measures do you take on your Profibus networks? Do you take special measures as grounding the shield of the profibus cable to mounting plate of the cabinet? If so, is the shield only connected to ground on the entrance and exit of the cabinet, or is it grounded at each profibus node? Do you install eqiupotential ground cables between the cabinets with a large cross-section (f.i. 10 mm2 or more)?
Or do you take other measures?
Did you ever have profibus problems? What was the cause, and what was the solution?
Thanks
Profibus: Yes, we ground the shield of incoming and outgoing profibus cable to the mounting plate of the cabinet.
Only at these points, even if there are more than one node in the cabinet. Anyway .. the profibus cable being pulled inside cabinet are off course properly separated from other cables, and only placed within cable trays with max 24Volt cables.
Eqiupotential: Yes and No. If I do the hardware design/cable sheet I always specify a 16mm2 cable to be pulled paralell with all prfibus cables.
Unfortunately not of all my colleagues are doing it.
Problems: Ohh yeah .. lots of
Some examples:
1.Poor connection of the shield of the profibus within the profibus connectors.
2.Profibus connectors of too bad quality, I prefer to use Siemens "Fast Connect" connectors whenever possible, never had any problems with these connectors.
3.Profibus cable not being separated properly from power cables along cable tray, the noise from the power cables (fed by a VFD) disturbed the profibus.
4.Profibus cable are pulled a too long distance, have to install repeaters or decrease baud rate to have a stable communication.
5.Missing equipotential between nodes caused alot of problem in a project a few years ago, we had the ground cable in our cable list .. but for some reason the electricians hadn´t pulled it. During first week of production we had ALOT of problems with nodes that for short time were not present. Electricians work day and night pulling the ground cable .. after connecting it to all cabinets/boxes .. TADAA .. no problems since that!
In this project we were using some older Siemens nodes (ET200U) also and I think that the earth connection of the backplane were not so good as of the newer nodes and that caused the big problems together with a not good enough separation of profibus cables from power cables (difficult since it was an existing machine line).
So my experiences is that you can never be too careful when working with design and commissioning of profibus networks.