We have a piece of machinery that uses a GE 90-30 rack system. It communicates to a pc with a touchscreen running Cimplicity via Ethernet. The HMI has been running flawlessy for quite some time now ( years) and have recently noticed that every once in awhile the screen graphics turn to black ( Like it isn't communicating) then everything ( data) will pop back a few secods later. I am wondering what would cause this, at first i am leaning towards maybe the cable is bad, so i may start there. Any other suggestions. Thanks
 
Hi jcraft

This is probably a stupid suggestion but are you sure it isn't that nothing is happening for a while and the screensaver is kicking in??

If not, then I would suggest checking the cable too.

Is it always "black" for the same amount of time?
Are there any other issues when it comes back from one of its 'blackouts'?
It might also be worth making sure there isn't a build of dust and **** inside the screen causing over-heating issues?

Cheers

;-)
 
The entire screen isn't going black, basically the entire graphics screen is shown it's just the data associated with the graphics is blacked out and not showing the values or some show xxx
 
Well that normally means that either the address that is trying to be read isn't there/is out of range OR you've lost comms (as you suspected).

So... you were right. Check the cable and connections both sides.

Also be wary of 'noise' causing interference.

I'm assuming that nothing has recently changed with the installation (i.e. have you added any new motors / mains wiring etc)?
 

Similar Topics

Easy, basic question... this is my first time linking 3 ABB vfds to an Allen-Bradley PLC using ethernet IP, and the odva Drive assemblies 123 and...
Replies
11
Views
2,489
Hi all ! I can't figure out how to setup the modbus RTU comm. to connect a Koyo DL250-1 CPU with a Panelview Plus 600 from Allen-Bradley. I use...
Replies
8
Views
3,959
Hi, First post, I am new to this forum. I tried searching with no luck. I am using an Omron PLC - CJ2M CPU32,and I am trying to get it to...
Replies
0
Views
2,395
Hello, I'm new to PLC programming and recently hit an I/O comm snag. I'm using a DirectLogic 205 DL250 PLC with an InTouch 7.1 HMI. The I/O...
Replies
7
Views
28,430
Good Day to all of you, this is my first post, i will try to explain as best as possible, english is not my natural language. I am performing an...
Replies
0
Views
36
Back
Top Bottom