You can't.

Since CompactLogix uses a tag database, not data files, then SLC has no knowledge of how to address the data.

You can however, use the CompactLogix to send the data to the SLC, using a MSG instruction. Set up the MSG for a "SLC Write" type of message.
 
Just to clear up ........ YES YOU CAN

Follow Mickey's link. You will see how to map an array in the 5000 to appear like a data file thast the SLC can read from or write to.

OG
 
Follow Mickey's link. You will see how to map an array in the 5000 to appear like a data file thast the SLC can read from or write to.

That's right. I made it reading and writing a ControlLogix with a PV Standard and it works, the clue is in the mapping.
 
An Apology

You can't.

Since CompactLogix uses a tag database, not data files, then SLC has no knowledge of how to address the data.

You can however, use the CompactLogix to send the data to the SLC, using a MSG instruction. Set up the MSG for a "SLC Write" type of message.

I can't explain what I was thinking about when I made that reply - of course you can read data from a ControlLogix as described. To make matters worse, I have done it myself many times.

The mapping handles the translation of a PLC5/SLC style data-table addressing to ControlLogix Array tags.

Sincerest apologies for the misleading information. Put it down to old age, overwork, or staying up too late, or just plain stupidity.
 

Similar Topics

Hi everyone, I try to have a Compactlogix L32e act as master PLC, so it will collect data from four SLC 5/04(int & string). The four SLC...
Replies
7
Views
5,139
I am working on setting up a Prosoft Datalogger model PLX51-DLplus-232. This unit will be collecting data from a SLC 5/05 on the DB9 port set to...
Replies
3
Views
103
I have a redundant ControlLogix being set up. This program reads a value from a remote site which happens to be SLC PLC. Rockwell mentions SLC...
Replies
2
Views
96
Hello, I have a ControlLogix redundant controller being set up. The program reads a value from a remote site which hosts a SLC PLC. Rockwell...
Replies
0
Views
80
Hi all, if I remember correctly, there is some way in a ControlLogix (or CompactLogix) where you can sort of map tags into SLC addressing format...
Replies
8
Views
1,155
Back
Top Bottom