You can't.
Since CompactLogix uses a tag database, not data files, then SLC has no knowledge of how to address the data.
You can however, use the CompactLogix to send the data to the SLC, using a MSG instruction. Set up the MSG for a "SLC Write" type of message.
Just to clear up ........ YES YOU CAN
Follow Mickey's link. You will see how to map an array in the 5000 to appear like a data file thast the SLC can read from or write to.
OG
That's right. I made it reading and writing a ControlLogix with a PV Standard and it works, the clue is in the mapping.
An Apology
You can't.
I can't explain what I was thinking about when I made that reply - of course you can read data from a ControlLogix as described. To make matters worse, I have done it myself many times.
The mapping handles the translation of a PLC5/SLC style data-table addressing to ControlLogix Array tags.
Sincerest apologies for the misleading information. Put it down to old age, overwork, or staying up too late, or just plain stupidity.
Hi everyone, I try to have a Compactlogix L32e act as master PLC, so it will collect data from four SLC 5/04(int & string). The four SLC...
5,160
I am working on setting up a Prosoft Datalogger model PLX51-DLplus-232. This unit will be collecting data from a SLC 5/05 on the DB9 port set to...
130
I have a redundant ControlLogix being set up. This program reads a value from a remote site which happens to be SLC PLC. Rockwell mentions SLC...
164
Hello, I have a ControlLogix redundant controller being set up. The program reads a value from a remote site which hosts a SLC PLC. Rockwell...
98
Hi all, if I remember correctly, there is some way in a ControlLogix (or CompactLogix) where you can sort of map tags into SLC addressing format...
1,177