Siemens - Changeing th DB values

alekbeck

Member
Join Date
Mar 2009
Location
Tønsberg
Posts
40
Hi everyone

I am using the PID function block (FB41 C) to regulate airflow. From my controll screen i want to change the P, I , D and gain values. Is is possible to write new values directly to the Data block from my controll screen ? If so how do i adress this in the program ?

I found the command "DB1.DBD0" , but this is DINT, my value is TIME

Hope someone understood my question !
 
Hi there
In fron if TI and TD of your FB41 you can directly enter time value. For example t#2s

Or you can create a DB with data type : TIME

So if your TI is DB1.DBD0 (with data type time) then you can change this value from variable table to whichever value you want anytime.
 
Okay thanx ! Can i alsow write to this adress from the controll screen (Made in citect) ?

This way i doent have to use so many MD adresses!
 

Similar Topics

The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
9
Views
160
Hello I have a s7-1200 and I would like to read the tags present in this controller with my controllogix controller. The two controllers don't use...
Replies
5
Views
142
Hi need help why this “failure 5 emergency stop “ appears at every startup in the morning ? Have to shut off main switch at least 10 times on...
Replies
19
Views
300
i have two plc 1. s7-1212dc/dc/dc ip; 192.168.0.1 2. s7-1500 1513-1pn ip; 192.168.3.2 i need to get data from plc1 to plc2. any idea how to do...
Replies
5
Views
112
Hi everyone hope you'll well. Is it possible for me to download a Crack version of tia portal v13..sorry to say this but the software is very...
Replies
5
Views
198
Back
Top Bottom