Hi,

How can I read and program for an analog input (4-20mA) from a Pressure transmitter. I'm using GE Fanuc's Versamax micro 23 point PLC.

Can anyone help me on this topic?


Thanks,

AbsimFan.
 
I guess that what you need is to scale you 4-20 mA signal into pressure value range of your transmitter.
Example 4 mA means 0 PSI and 20 mA means 150 PSI, if you transmitter has a range 0-150 PSI.
 
I'm not overly familar with the GE series of PLC's but the first question i have for you is have you made sure that the PLC you selected has a 4-20ma input? i looked over a listing of the versamax series micros and alot of them that have analog inputs seem to be in the 0-10vdc range - i didnt see any that specificly listed 4-20mA
 
If the PLC analog input is limited to 0-10 vdc you can purchase converters/isolators to convert the 4-20 madc to 0-10 vdc.
 
Reply for yesterday's post

I'm not overly familar with the GE series of PLC's but the first question i have for you is have you made sure that the PLC you selected has a 4-20ma input? i looked over a listing of the versamax series micros and alot of them that have analog inputs seem to be in the 0-10vdc range - i didnt see any that specificly listed 4-20mA


:geek: The versamax micro Expansion module IC200UEX624 has both voltage (0-10V DC) & current (4-20mA) input options. Also Versamax micro 23 Point controller has 2 inbuilt AI (optionally 0-10V DC and 4-20mA DC.
 
1.configure the analog input block to 4-20 ma mode.
2. Check the address of the analog input in the hardware configuration of the module.
3. Use a scale int block. give the address of AI at 'IN' of the block. Give IHI-32767, ILO-0 & OHI- high limit of the device & ILO- lo limit of the device.
4. Use a register at Q.
5.Now based on the input from the device, you will get the reading in the register.
 

Similar Topics

I am setting up a new system and have an s7 1214 plc with an sm1231 4x AI (6ES71231-4HD32-0XB0). It is configured for 0-10v and has no faults in...
Replies
5
Views
1,167
Hi all! Is someone can help me to understand what they means ? This is the only info I could find on my device : With this module is possile to...
Replies
5
Views
2,355
1762-IF2OF2 Analog Input Problem I use Micrologix1100 and explantion 1762-IF4 and...
Replies
2
Views
2,610
IM trying to find a cheap way to read system voltage using a 0-10 vdc input. my working voltage range is from 10-20 volts. Is there a voltage...
Replies
9
Views
4,539
Hi All, I am trying to collect data from an analog switch using AD module in a FX2N series PLC. I have attached my small code that I am using to...
Replies
14
Views
20,385
Back
Top Bottom