Hi. I am using RSView Studio ME (v4) to program a PV+ connected to a SLC500.
Is it possible to create one analogue tag (example N7:10) and then get the PanelView to see it as 16 x Bits ???
(example N7:10/0 to N7:10/15)
I need to display 16 x Indicator Lamps based on the Bits within the Word.

OR, do I have to create 16 individual Bit Tags.

Thanks in advance for any replies.
Alan
 
In my case this a digital tag, but as you can see, you can divide your 16 bits word into a bit by bit tag.
This is the way to do it, in this case this is a push button ( K1 ).

pv+&slc500.JPG
 
Hi Bill. This is interesting... you seem to have entered the raw PLC address directly into the "Connections" box, rather than setting up a "Tag" in the Tag editor. This could save a lot of time. I like it.
Thanks
 
Hi Bill. This is interesting... you seem to have entered the raw PLC address directly into the "Connections" box, rather than setting up a "Tag" in the Tag editor. This could save a lot of time. I like it.
Thanks

PV+ and FTView both support "Direct Referencing" of the PLC Namespace, without actually creating tags. It is useful to many people, and can be very convenient.

Personally, except for EXTREMELY Q & D (Quick and Dirty) updates or applications, I can't stand the Direct References, but that is personal preference :).

I generally set up and edit my Tag Database in Excel, and then import it whole into View Studio.
 
Thanks rdrast.
Getting back to the original question, if I do use Tags, then is it just a matter of putting a... /n after the tag name ?
( n = the bit number)

Regarding using Excel... If I export an existing tag database, add some new tags to it and then import it back, is this likely to screw up any of the screen objects that have already been configured. ? (assuming I don't change any of the originals)

Thanks for any replies
Alan
 
Just for reference:

N7:0/0 is (N7:0 & 1)
N7:0/1 is (N7:0 & 2)
N7:0/2 is (N7:0 & 4)
N7:0/3 is (N7:0 & 8)
N7:0/4 is (N7:0 & 16)
.
.
N7:0/14 is (N7:0 & 16384)
N7:0/15 is (N7:0 & -32768)
 
Just for reference:

N7:0/0 is (N7:0 & 1)
N7:0/1 is (N7:0 & 2)
N7:0/2 is (N7:0 & 4)
N7:0/3 is (N7:0 & 8)
N7:0/4 is (N7:0 & 16)
.
.
N7:0/14 is (N7:0 & 16384)
N7:0/15 is (N7:0 & -32768)

I've had to do this in RSView32 when I ran out of tags. Cheaper than having to buy more tags. Not really an issue in FT View since it is not tag based.
 

Similar Topics

I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
80
Hi Everyone, Currently we have three plants running with Controllogix PLCs (L72, L73, L74). In each of these plants we have 2 FTView SE...
Replies
0
Views
54
Hello All! Ok, we got a Work cell from a Integrator that is sending saved scanning data from the PLC to HMI (Panel View Plus) when I look at this...
Replies
3
Views
81
Hello everyone. This is more of an HMI issue. I have a new PanelView Plus 7 Series B. I am using the alarm list object to display the fault...
Replies
0
Views
91
Hello, I made a change in alarm setup in factory view studio, where I changed a alarm message text. After that I made a run application and...
Replies
0
Views
132
Back
Top Bottom