Greetings,
I would like to share few tips on troubleshooting I/O cards and PLC in case of Emergency.

I has voltage / grounding problems due which S7-300 analog cards and 313C failed, replaced it with new one again it failed, later on analysing the root cause , found problem was with Electrical grounding ,
Since the plant had to be started, having sacrificed the spare too.
On opening the Analog card and checked with mutlimeter the components, found SMD fuse had blown, I soldered and brought out those two wires and connected to external fuse link outside and it worked and same also happened on S7 313C PLC ,cause all of them were out of warranty.
The similar sitauation happened in Modicon Digital input card, ,as one of the channel was accepting input, foung SMD 2.2K resistor blown , replaced it with 2.2K carbon film resistor, found working fine and it toke me 30min to troubleshoot and put that back into service.
hope this is useful, when running out of spares.

Good luck.
Jay
 

Similar Topics

Hello, I got some second hand 5069 cards to use as temporary cards until Allen Bradley shortages are over. They will be going in the same PLC but...
Replies
9
Views
3,380
I currently use a Safety module from Wieland and have been asked to use a GuardLogix PLC. I have two outputs setup in the controller to output...
Replies
4
Views
1,682
I know you can change out ControlLogix cards with the rack powered. And I thought that you could not do it with a PLC-5, but a colleague at work...
Replies
13
Views
4,140
Hi there, Wondering why my Analog cards may not be working all of a sudden. I am using the CLICK PLC Series. I recently changed the main unit...
Replies
11
Views
2,257
Hello Friends, I need to know that. In Delta PLC's, In which model we can connect max cards for increase digital inputs, outputs, analog inputs...
Replies
1
Views
1,475
Back
Top Bottom