When wireing 24 vdc control circuits i know that it supposed to be blue and blue/white stipe but i see some machines that have blue and white/blue stripe.

My question is which is correct or are both? If both which is best?

What is the typical application or use of the other color?
 
Can't be sure I speak for everyone, but for us blue with a white stripe is the lower potential on an ungrounded circuit (ie +/-12V) while white wire is grounded neutral, the blue stripe indicating that it is used in 24VDC control.
 

NFPA 13.2.3.2

The use of other colors for the following applications shall be as follows:
(1) WHITE with BLUE stripe for grounded (current-carrying) dc circuit conductors.

Exception No. 2. Where the identification of machine power and control wiring is such that compliance with the mandatory color codes is too restrictive for specific applications, it shall be permitted to use additional identification at selected locations as an alternative. This means of identification shall be permitted to be by separate color coding, marking tape, tagging, or other approved means and shall be permanently posted on the inside of the main electrical control panel enclosure in a visible location.
--------------------------------------------------------

Note that this says grounded current carrying conductors. If you don't ground your DC power supply 0V then it might not apply.


Of course, if you are buying wire from automationdirect, then you might have to settle for blue with a white stripe instead. Just claim its white wire with a really big fat blue stripe. 🍺

In a pinch I've stripped my own using white MTW and a blue permanent marker. A marker with a big flat tip works well. Put on a rubber glove and hold the wire against the marker tip with one hand while pulling it through with the other hand. You can quickly stripe a couple of dozen feet. Works in a pinch if you run out or need just a few feet. I wouldn't do it for a big job though.
 
Last edited:
Germans use blue blau and brown , brauwn, with umlots. USAF uses black for all DC common and red for DC positive. GM and Ford use black and red.

The above regulation says you can use any label you like as long as you declare it.

"Exception No. 2. Where the identification of machine power and control wiring is such that compliance with the mandatory color codes is too restrictive for specific applications, it shall be permitted to use additional identification at selected locations as an alternative. This means of identification shall be permitted to be by separate color coding, marking tape, tagging, or other approved means and shall be permanently posted on the inside of the main electrical control panel enclosure in a visible location."

Translation, use what works for you and post a note in the cabinet.

Of all the companies I have worked for and with, I have not seen any standard used consistantly except for the Germans. They are consistant.

The American companies I worked with, use the wire they have on the shelf or what the supplier has in stock the day they order.

Once the spec called for colored wire to be used inside the cabinet. We looked in the cabinet. It was wired in all black MTW for everything. The panel builder said " This is North Carolina, that IS colored wire."

We hooked it up and put it in production and no one mentioned wire color again.
 
Does anyone know where to get White w/blue stripe and white w/orange stripe colored wire?

Any electrical distributor worth their salt can get it, they may not stock it, but they should be able to get it. We usually order the striped wire in 2500 ft rolls, usually a couple of rolls a time. It lasts a while.

Automation direct has blue wire with a white stripe if you want to use that as an option. Newark will stripe most of their wire if you request it, but Newark wire is usually a lot more expensive than your local wire house will be.
 
Once the spec called for colored wire to be used inside the cabinet. We looked in the cabinet. It was wired in all black MTW for everything. The panel builder said " This is North Carolina, that IS colored wire."quote]


two-cats-reflect_bw-420.gif


Is black a color?
No, black is not a color; a black object absorbs all the colors of the visible spectrum and reflects none of them to the eyes.

 
Once the spec called for colored wire to be used inside the cabinet. We looked in the cabinet. It was wired in all black MTW for everything. The panel builder said " This is North Carolina, that IS colored wire."quote]


two-cats-reflect_bw-420.gif


Is black a color?
No, black is not a color; a black object absorbs all the colors of the visible spectrum and reflects none of them to the eyes.


in visible light, black is the absence of color. in pigments, it is the addition of all colors. regardless, this is just a cheeky answer to your cheeky retort. =D


for the record, our UL508 shop does all 12 and 24vdc with blue and brown wire. usually it is specced out that way by the designing engineers.
 
......GM and Ford use black and red.......

In the automotive world, Red is 110vac and Black is any other current carrier over 50v, typically 480vac. Blue and blue/wht or wht/blue is 24vdc. Stripes are added to any color wire for specific use and can deviate depending on the facility.
 
Per NFPA 79

It goes with the ORANGE color of ungrounded ac circuit conductors which remain energized...


(2) WHITE with ORANGE stripe for grounded (currentcarrying)
ac circuit conductor, which remains energized
when the main supply circuit disconnecting means is in

the off position.
 
If i remember correctly the OSG (UK) lists a number of colours you can use for DC + and blue for DC-... Don't have the book handy otherwise i would state the recommendation
 

Similar Topics

Good Morning, I am building a panel that has 120VAC, 24VDC, 12VDC, and 5VDC, and was wondering if anyone had any ideas for wire colors. I have...
Replies
10
Views
3,103
So, I am covering for a colleague who is out this week, and I started to check out a control panel he had designed. To my surprise, I opened the...
Replies
8
Views
6,541
I got a panel in today built in the U.S. and it has Brown wire for 24 VDC + and Blue wire for 24 VDC-. Is this the European standard? I have seen...
Replies
17
Views
4,728
I've read the EN60204 section on wire colors and one thing is still not clear to me. What wire color is used for the grounded DC current...
Replies
11
Views
3,571
Have a project going to the UK, not exactly sure where yet but in the specs they call out the following wire colors. Brown: All line conductors...
Replies
3
Views
2,613
Back
Top Bottom