Hey guys I have a question. I just installed a 1746-NT4 with a supposed J thermocouple. I tried scaling it according to the manual but my readings were not linear. I have never used this module on a slc so i don't know if my issue is because the cart is bad or the TC -346° to 1400° is the suggested scaling but i have to put in 120 - 1382 to get it to read correctly any suggestions?
 
Last edited:
Post your .rss file and someone can take a look at your configuration

See pictures below for a typical configuration based on your description.

With the configuration below you will get a direct deg Fahrenheit data from the card.
Note different scaling choices if you want something other then a direct temperature read out.

NT4scaling.jpg NT4Config.jpg
 
Last edited:

Similar Topics

Hello everyone. This is my first time to post a question in this forum. I would like to seek your help on how i can create program on a SLC500 cpu...
Replies
8
Views
2,699
Hi ! I need to add 2 thermocouples on a 1746-NT4 card. The program was create on RSLogix 500 Ver.3.0 so they don't use the advanced config to...
Replies
10
Views
2,803
Hi, I have a PLC with SLC5/04(slot 0), 1746-NT4(slot 1), 1746-IB16(slot 2) and 1746-OW16. So, I need read the temperature all the time and when...
Replies
17
Views
4,485
I am troubleshooting this plc rack with 1746-NT4 cards. The problem is that some of the inputs are workings (solid green), some not(blinking...
Replies
2
Views
2,146
hi everyone, i have AB 1746-nt4 card but with missing cjc thermistor(both side) , how could i buy the cjc?,any special specs should i follow on...
Replies
5
Views
3,089
Back
Top Bottom