what is the correct method of driving multiple motors from a vfd with centralized control? example is 460v 3ph to vfd or xl contactor with multiple overloads(for each motor) to motors whose locations are up to 280 feet away from the control cabinet. 1 conduit with all of the leads or multiple conduits for each motor or other. I have 17 units in need of attention as we have smoked about 12 motors and 3 vfd's in our current configuration.
thanks Dan
most of the motors are .5hp 1150rpm there are several refrig units. some have 3 motors per unit some have only 2 and some have up to 4. motor failures on all systems.
yes the drives are sized for above total hp for the units they are driving. most of the damage has been cooked motors. but when i have a fan fail there is nothing to keep the fan from running freely. (ice, debris ,ect)
I cannot change the layout without a lot of $.
how do I correct this problem with the least cost.
motor overloads are in the vfd cabinet but were bypassed by the installing contractor. only 3 lines running to each fan unit and distributed to each motor at the end of the line.
tntmachine,
I'm sure our resident expert DickDV will come by soon. If you wouldn't mind can you clarify a few things? It will help him and us give you a good answer.
1. You have a centralized control cabinet with VFD's inside correct?
2. You have multiple motors on some or all of the VFD's?
3. On the motors that are ganged together on one drive
3a. They are 1/2 hp units
3B. Some are 280 feet from the VFD, correct?
3c. The control cabinet has individual overloads for each motor but the contractor has bypassed them and only installed one set of "T" leads to the group of motors, correct? Do you have any leverage on the contractor? Details on the overloads would be good also ie. pilot duty, IEC style w/phaseloss protection, ect. ect.
3d. Are you multiple motoring the fan motors only?
3e. What is the input voltage on your VFD's, and are your fan motors 240 / 480 volt units? And are they three phase units (those pesky refrigeration folks sometimes use single phase 480 fan motors)?
4a. In your first post you mentioned an "xl contactor with multiple overloads". Is this your present configuration?
4b. Can the "xl contactor" disconnect the motors from the VFD at any time when the VFD is running (details please)?
Edit: I see Dan has asked more questions, they need answers too.