I am having trouble logging online to a rs1000. I am using the standard rs232 cable but I must have the wrong node settings or something..the error I get is the path/node error. Can someone please help
 
I am having trouble logging online to a rs1000. I am using the standard rs232 cable but I must have the wrong node settings or something..the error I get is the path/node error. Can someone please help


No such thing as rs1000. Do you mean ML1000?
What cable are you using, complete catalog number?
What driver are you using in RSLinx?
The more info the better the help.
 
Driver is for the 232 cable and I am using that particular one. I am not near it at the moment to get the complete catalog number. Is there an auto config feature that RSlinx can recognize the PLC? I'm not real AB savvy by the way.
 
Please refer to the following post
http://www.plctalk.net/qanda/showthread.php?p=195474

In your RSLinx do the following:
1. no setting need in your PLC
2. just use a cross cable to connect between your PLC and PC
3. goto Communication>Configure Drivers
4. select RS-232 DF1 devices and click Add New... button
5. select the right Comm. Port for your PC
6. click the Auto-Configure button
7. if very thing is fine you should see the Successful message and your PLC will appear on the RSLinx
 
In your RSLinx do the following:
1. no setting need in your PLC
2. just use a cross cable to connect between your PLC and PC
3. goto Communication>Configure Drivers
4. select RS-232 DF1 devices and click Add New... button
5. select the right Comm. Port for your PC
6. click the Auto-Configure button
7. if very thing is fine you should see the Successful message and your PLC will appear on the RSLinx

Very good.... all but number 2, the cable is not a cross cable, you need a 1761-CBL-PM02
 

Similar Topics

Hi, I have a ControlLogix system with 1756-IF16 analogue inputs. I can't scale the inputs at the card as there is a requirement to facilitate...
Replies
14
Views
359
Dear community, I am trying to find a tool for Allen-Bradley PLCs similar to SiVArch for Siemens PLCs to automatically generate faceplates and...
Replies
0
Views
92
Hi everyone, new to forum. Since very long time i having issue with 1734-AENT module, after some period of time its keep stuck in error (simmilar...
Replies
16
Views
608
Hello, I am new here. I am trying to find good places to sell some surplus items that I have that isnt through ebay. Does anyone have any sources...
Replies
6
Views
427
Hi all, installed on chassis A17 an A/I from Allen-Bradley , problem is what ever I do , all channels are sticked on value 39.9 and cannot change...
Replies
1
Views
145
Back
Top Bottom