when scanning program goes from left to right and top to
bottom but what happens when there is a branch on the
output.
Does the top part of a branch on output get turned on and
then next scan unlatch if you want like a one shot?
or is this possible?
------------0
------------
------------0
Thanks Mike
 
Depends partially on your PLC.

An easy way to see the scan order is to use your programming software. Switch the view to "Mnemonics". Some software has this feature.

The order the code is listed is also the scan order.

If the branch is legal within your network, the entire branch will be scanned each scan.

Try posting an example, include the PLC type will get you better answers.

Hope this helps
 
Bluebyu
The thing is that people who are able to use Mnemonics are not likely to be the ones who are confused by this. Branches are generally representations of Assembler Push and Pop instructions but these instructions are effectively invisible to people who have only used ladder. The answer is simply education.
 
sometimes a picture helps ...

Greetings Mike ...

let's assume (gosh I hate that word) that you're talking about an Allen-Bradley system ...

here's the first part of your question:

when scanning program goes from left to right and top to bottom

unfortunately that is NOT absolutely correct ... rather than go through a lot of mumbo-jumbo about what actually DOES happen as the processor executes the rung, I suggest that you use the ASCII (mnemonic) mode in RSLogix to display your rung and track down the actual instruction-by-instruction sequence of execution ... this is the technique that bluebyu was recommending in his post (above) ...

I've posted an example figure below that might be helpful ... you might also want to take a look at post #20 in this thread:

http://www.plctalk.net/qanda/showthread.php?p=98323&postcount=20

secret handshake: for your purposes, you can just skip over any "branch-type" instructions (BST, NXB, and BND) and simply concentrate on how the PLC processor executes everything else ...

going a little bit further ... you went on to ask the following:

but what happens when there is a branch on the output. Does the top part of a branch on output get turned on and then next scan unlatch if you want like a one shot? or is this possible?

I'm not sure that I understand what you're asking there, so if you're still having problems after all of the dust settles, I suggest that you post again with some more detail – and ideally a screen shot of whatever rung construction is confusing you ... I'm sure that the forum members can help you sort it all out ...

also ...

something about the way that you phrased your question leads me to think that you might have some serious misconceptions about exactly what is going on during the processor's scan sequence ... (believe me, you would NOT be alone) ...

my point is this:

no offense intended, but if you think that the "outputs" on your rung (specifically the OTE, OTL, OTU instructions) are actually "turning things ON or OFF" - or else "latching things ON" - etc. then you're making ladder logic a lot harder to understand than it needs to be ... there's a MUCH easier way to look at the PLC's operation than that – and fortunately that easier way happens to be more accurate too ... if you're confused by any of this, then I recommend that you watch the series of YouTube videos available on the "Sample Lessons" page of my website ... you should watch these IN ORDER and see if the basic information there helps you gain a better understanding of what's actually going on "under the hood" of an Allen-Bradley PLC ...

I hope this helps ...

ASCII mode.JPG
 
Last edited:

Similar Topics

This should be a pretty easy question, would just like to have it explained a bit so I can understand it. In the attached program, why does the...
Replies
15
Views
4,719
Hi All, In most older PLC's of all makes the sequence within the PLC was to scan the Inputs then Work the logic out and then set the Outputs. (3...
Replies
2
Views
1,287
Hi all, I primarily use AB PLC's, and have a reasonable understanding of the way they scan their logic. I've done a few smaller projects on...
Replies
18
Views
5,540
I know that an Allen-Bradley PLC will scan every input first and store them in memory, then solve the ladder, then update the outputs. I'm...
Replies
3
Views
4,565
The question revolves around what happens if I have the same output coil on multiple rungs. In a SLC504 PLC, the following code results in the...
Replies
18
Views
6,244
Back
Top Bottom