Hi all,

Can Prosoft MVI56-MCM modbus card be loacted in the AB Controllogix remote rack connected by controlnet network? or it must be in the local rack? Thanks.
 
Yes, the MVI56-MCM may be located in a ControlNet or EtherNet/IP linked remote chassis.

However, the MVI56-MCM connection is very large and will consume a great deal of bandwidth on the network.

Prosoft builds a version of the module that is specifically designed for remote ControlNet chassis, called the MVI56-MCMR.

The "R" stands for "Reduced Data Block".

ProSoft recently released an enhanced platform for the MVI56 modules, including a MVI56E-MCMR reduced data block module.

http://psft.com/prosoft/products/for_rockwell_automation/platform/controllogix/mvi56e_mcmr
 

Similar Topics

The MODBUS module is attached w AB PLC. Port 1 (master) has problem in communicating w Mits PLC while Port2 is ok. Port1 can write data to Mits...
Replies
7
Views
3,050
can we use Allen-Bradley 1756-L55 controller to communicate with MVI56-MCM Modbus communication module
Replies
4
Views
1,974
Dear Members, I need to ReadData from Slave Device Modbus Address 48001 by using MVI56E-MCM which set as Master. How can I do it? I read the...
Replies
3
Views
1,904
Dear Members, I need to ReadData from Slave Device Modbus Address 48001 by using MVI56-MCM which set as Master. How can I do it? I read the...
Replies
0
Views
1,489
Dear Members, I am using AB PLC with MVI56-MCM to read data from modbus address 40100-48100 from ABB Drive. How could I do it with one MVI56-MCM...
Replies
1
Views
2,115
Back
Top Bottom