I've got a customer who wants me to calibrate the thermocouples on their oven. These thermocouples(K-type) are tied to Flex I/O 1794-IRT8 modules. I have a couple of questions about this.
Is it necessary to calibrate the IRT8 module itself (it is supposed to be calibrated from the factory) or just to apply an offset for each thermocouple after testing it accuracy? My problem is I am having trouble finding a reasonably priced mV source to supply the needed +/- 320mV AB calls for in the calibration procedure (see attached Pub 1794-6.5.12 Section 6). That value seems a bit high to me anyhow for a thermocouple.
I intend to check the thermocouples with a dry well calibrator to determine if an offset needs to be applied. Would this be the correct way of doing this?
Thanks
I've got a customer who wants me to calibrate the thermocouples on their oven. These thermocouples(K-type) are tied to Flex I/O 1794-IRT8 modules. I have a couple of questions about this.
Is it necessary to calibrate the IRT8 module itself (it is supposed to be calibrated from the factory) or just to apply an offset for each thermocouple after testing it accuracy? My problem is I am having trouble finding a reasonably priced mV source to supply the needed +/- 320mV AB calls for in the calibration procedure (see attached Pub 1794-6.5.12 Section 6). That value seems a bit high to me anyhow for a thermocouple.