Calibrating Thermocouples
DoubleL
Jul 2004
Georgia
47
Hi Guys,
I've got a customer who wants me to calibrate the thermocouples on their oven. These thermocouples(K-type) are tied to Flex I/O 1794-IRT8 modules. I have a couple of questions about this.
Is it necessary to calibrate the IRT8 module itself (it is supposed to be calibrated from the factory) or just to apply an offset for each thermocouple after testing it accuracy? My problem is I am having trouble finding a reasonably priced mV source to supply the needed +/- 320mV AB calls for in the calibration procedure (see attached Pub 1794-6.5.12 Section 6). That value seems a bit high to me anyhow for a thermocouple.
I intend to check the thermocouples with a dry well calibrator to determine if an offset needs to be applied. Would this be the correct way of doing this?
I spend may hours per year calibrating temperatures, flows, pressures etc. A drywell is certainly the best, here we have the drywell checked once a year & obtain a calibration cert to UKAS standard (this is part of our procedures).
Cable lengths, types, cards etc. can all introduce errors.
Most plc cards do not come with certificates just a general specification, so I check all the way through from sensor to display the offset/zero (or zero/span) of the whole loop is checked, I insert the probe in the drywell, also a calibrated probe in the drywell (this gives a true reading of the temperature at the probe tip in the block), wait until it stabilises then adjust the zero or span acordingly, this is done at both ends of the range & repeated a number of times as adjusting the zero affects the span & vice versa.
our specs in the food industry are +- 0.7 Degrees C, however for ovens, heaters it probably won't matter quite so much.
We are audited every year & it is important that we can produce paperwork to prove the procedures are followed.
Hi all, Probably a bit out of my depth here as I'm not an instro but just wondering if someone could provide some clarity on calibrating/scaling...
3,073
I know this is very far off subject, but was hoping someone here could lend a hand. I have been asked to start calibrating belt scales for...
19
3,818
I have a vacuum furnace running an Allen Bradley SLC 5/03 with a PV 550, I am new to PLC's and using RSLogix 500. My issue is that the control...
35
4,924
this is one of the assignment that i have been given in my training course, i really don't understand the way to do the calculation required for...
11,625
I am looking for information on the proper calibration of an 1756-IF8 analog input card, preferably the wiring of the voltage source. Rockwell...
8,069