Hi

I am running RSView32 with an SLC504 PLC project, I would like to retrieve my device information (Tags) using DDE/OPC instead of using the standard direct drivers. Althought I am configuring a DDE/OPC topic on RSLinx and creating a project on RSVIew32, I cannot address my tags to the SLC504.

Can anyone suggest me the right procedure to accomplish this?

Thank you !
 
Here are a couple of things you can try.

Run the OPC test client that comes with RSLinx Tools to
verify your topic is configured correctly. If you can read registers from the PLC with the test client your OPC topic configuration is correct. Next, I would insure your Node is set up correctly in RSView.
Be sure to check the enabled box. In the Server box enter the server as RSLinx OPC Server. Select Local if RSLinx and your RSView app
are running on the same box. And enter your topic name you created
in RSLinx into the Access Path Box. You should then be able to create tags using this node to locations in your PLC.
 

Similar Topics

I’ve been put in charge of designing an excel spreadsheet for one of our customers (running RSLogix software). This spreadsheet is meant to get...
Replies
9
Views
4,523
Hello Guys, I am trying to test HMI in TIA Wincc Professional V13 with my virtual machine with Rslogix emulator. Wincc is using OPC to...
Replies
0
Views
1,410
Hi, I have attempted to move some software that runs in XP from an obsolete APC to a new windows ten APC. The new APC is running VMware and I...
Replies
3
Views
1,939
Hello All, I have a system of 2 PLCs Siemens CPU 315 - 2PN/DP (with a program Simatic S7 V5.5) and PC station runs Siemens OPC server Simatic net...
Replies
20
Views
7,426
Hi; I had designed an HMI in RS View32 Works and an SLC-5/05 had connected with that HMI via direct driver. Now as per requirement, i need to...
Replies
4
Views
2,814
Back
Top Bottom