Siemens OPC Server Help After Moving to a VM
antsrealm
Dec 2010
Brisbane
207
I have attempted to move some software that runs in XP from an obsolete APC to a new windows ten APC. The new APC is running VMware and I have virtualised the system and moved it across with minimal fuss.
The one problem I do have is that the configured OPC server is not communicating with the PLC and I know next to nothing about it.
The old APC had two ethernet ports. One was a CP-1612 card and one was on the onboard NIC.
The PLC seems to communicate via the CP-1612 and I think the other is used for the plant comms and winvnc etc.
the new advantech APC has two onboard ethernet ports and I am attempting to use those to communicate in place of the CP-1612.
It looks like some of the communication configuration removed itself when it saw that the card was missing. In the station configuration editor it said "the module was removed from configured operation". This was a IE General type. I had manually added it again but the status indicator is grey and it has loaded default parameters.
Can someone give me some advice in regards to this. I have looked at everything but I'm obviously missing something. Is it possible to use the regular NIC and what areas do I need to look in to correct that change in hardware.
Thanks,
An OPC server installed in a computer has two sides, one side communicates with the PLC or PLCs and the other with OPC clients, surely in the previous installation there was an interface for each side, and the same scheme should be kept in the new installation.
The VM need also the two interfaces configured each with the correct IP, Mask, gateway, but I do not know how to do that in VMWare ... I do not have experience about this
But if I remember correctly it is not possible to use the same IP in the VM and in the host computer, therefore now on the side of plant comms the OPC server will have a different IP than winvnc or other services installed in that computer.
Exactly what version is Simatic Net on the PC ?
The usual method to be able to reach out onto the physical network, is to bridge a virtual ethernet adapter to a real ethernet adapter.
Assign the IP address of the virtual adapter to be in the same subnet as the real adapter but not the same IP. 192.168.1.10 and 192.168.1.11 for example.
It is also a good idea to specify the real adapters MAC address to the virtual adapter, but it should not actually be necessary.
If you have done the above (either ethernet interface) then Simatic Net can connect to the PLC, if you can ping the PLC.
So, that is the test you should perform.
Thanks,
Your original Simatic Net project was probably configured with the CP1612. I don't think you can just fix it in the station configuration editor, you need to fix it in the original project where the PLC comms were configured.
Hi all, I have a CPU315-2 PN/DP with a CP card, which is CP343-1 Lean. I have a PI server and am trying to connect to the Lean card. I can ping...
3,739
Hello everyone, We have a customer who has reinstalled an Acronis backup of his PC but in Station configurator he has a red cross on OPC Server...
1,579
Hi all! I found interesting opc server from fastautomation.it But with lack of documentation... It is called Fast Spa OPC server for siemens s7...
1,962
I connected s7 300 plc to pc via siemens mpi usb adapter.I used simentic manager and view the data.It is working with simetic manager.But i can...
3,033
Hello All, I am having trouble setting up a S7-300 MPI connection using Simatic Manager 5.5. I am trying to use an OPC server with a S7 MPI...
3,905