Siemens CP343-1 Lean S7 connection to OPC Server
orense
Apr 2006
Norway
196
Hi all,
I have a CPU315-2 PN/DP with a CP card, which is CP343-1 Lean.
I have a PI server and am trying to connect to the Lean card.
I can ping the card so I know the cabling is working, but I am unable to connect using the PI connector for S7 protocol or via OPC UA.
I have used the default port number 4840, but am wondering if I should use 48010 instead.
Does anyone have any advice on this?
Thanks for that. Will try once I am back on site tomorrow.
I am using the CP in an extended rack built on a IM361 module, so the rack is 1, slot 11. The CPU is on rack 0 and slot 2.
Are there any other details you were thinking of?
There is not much more to specify, except the IP address, at least not in the CP configuration.
It doesnt matter that the CP is in a different slot.
You must specify the rack/slot of the CPU, and it is always 0/2 on an S7-300.
I think that the expansion IMs for S7-300 comes in versions with and without K-bus. Or is it for S7-400 ? I dont remember. Cant check it right now since I am away from my work PC. It could be worth checking that you have the right IM. Can you go online with the CPU via the CP ?
Pretty sure that's the 400, with two busses. As far as I know, S7-300 has only 1 bus, and I think it's pretty much crappy MPI.
Since you have PN/DP CPU, you could try to connect CPU's IP. If it connects to PLC port then you have error somewhere
Hello, I have a very similar setup, with CPU313C-2DP and a CP 343-1 Advanced. I am using the settings as explained by JesperMP. I hope the screenshot below will be helpful. Even confirmed with a non-Siemens tool that communication settings are correct.
The S7-300 also has both P-bus and K-bus, with the K-bus being essentially MPI. Outside Siemens not much is known about the P-bus but it is used to address the regular I/O. Years back I think that I saw someone post about it working the same as the backplane on S5-100U.
IM360 + IM361 connects both K-bus and P-bus.
IM365 connects only P-bus.
Huh, good to know. Thnx
Hi again,
A small update on this.
Seems like the infrastructure on the outside between the plc and our Scada goes through some firewall, where our IT department first has to determine how they need it to work. So for the moment I’m a bit stalled on this. I’ll bring it back up if needed when I’m getting around to having the OPC in the Scada reading data.
Thanks for now
Hi everyone, I have recently installed Siemens CP343-1 lean Ethernet modules (firm V3) on existing production line machine PLCs. Installation of...
7,693
we are trying to make tcp conn. between these 2 cards, untill now without result. maybe it is not possible anyway, does anybody expirienced the...
2,197
Hi! I have a question regarding ethernet communication with a Siemens S7-312C and 343-1 Lean. For some time I´ve been using the S7NetPlus...
3,302
I have a CP343-1 Ethernet module but it is missing the connector to supply 24VDC. Anyone know what the part number is for this connector (either...
1,950
Hi, Is the CP343 Lean module's performance affected by the PLCs scan time? The HMI uses ISO over TCP protocol but when there is a long scan...
3,561