jimlong
Member
Hello,
Working on a project at the moment where a newly laid underground swa cable 300 metres long ,3 X 35mm squared appears faulty and is giving some unusual readings on
insulation resistance tester, 1000 volt dc test voltage.
The readings are as follows:
Armour - Earth core >2000Mohms-ok
Armour - Blue core 1000-2000ohms
Armour - Brown core 1000-2000ohms
Earth core - Blue core >2000Mohms-ok
Earth core - Brown core >2000Mohms-ok
Blue core - Brown core 1000-2000ohms
Cable buried 1 metre deep in sand.Is it possibly faulty manufactured cable. Should have meggered it b4 laying it.Would 1000 volt dc test break down fault to a dead short.Tried reflectance but no good as it requires a dead short or open circuit to determine location of fault.Any help
Conclusion:
Earth core ok.Armour,brown and blue all problem.
Working on a project at the moment where a newly laid underground swa cable 300 metres long ,3 X 35mm squared appears faulty and is giving some unusual readings on
insulation resistance tester, 1000 volt dc test voltage.
The readings are as follows:
Armour - Earth core >2000Mohms-ok
Armour - Blue core 1000-2000ohms
Armour - Brown core 1000-2000ohms
Earth core - Blue core >2000Mohms-ok
Earth core - Brown core >2000Mohms-ok
Blue core - Brown core 1000-2000ohms
Cable buried 1 metre deep in sand.Is it possibly faulty manufactured cable. Should have meggered it b4 laying it.Would 1000 volt dc test break down fault to a dead short.Tried reflectance but no good as it requires a dead short or open circuit to determine location of fault.Any help
Conclusion:
Earth core ok.Armour,brown and blue all problem.