I have problem on my DHRIO connection between ControlLogix5000 and SLC5/04.I found the DHRIO installed is have a higher revision than the project software.So,I have plan to replace with the same revision.What I want to ask is if I remove the module and replace it,do i need to re-schedule it in RSnetworx ?since the processor and the DHRIO are on the different Rack and using ControlNet Module.

Thanks,
 
You don't have to replace the 1756-DHRIO. All you have to do is change the Electronic Keying selection to "Disabled" for the Connection to the 1756-DHRIO.

This will not require rescheduling of the network.
 
and if you're having communications issues, double-check the termination resistors ... I've found that the DHRIO is EXTREMELY picky about that subject ...

specifically, "blue hose" lab equipment that I have been using successfully for years without ANY resistors at all now suddenly gives all sorts of problems when I connect it to a DHRIO module ... I've even found that the cable from my PCMK card for DH+ communications won't always work reliably unless I also connect a 3-pin plug with a terminating resistor to the other A-Channel port ...
 
I'd like to amend my comments; I use "disable keying" only when I am troubleshooting.

The correct setting when you have a module that is newer than your software supports is to set the I/O connection for the closest available version, then set the connection for "Compatible keying". That is the standard procedure for 1756-DHRIO modules and it should work for you.

If your 1756-DHRIO is only being used for DH+ communications and not as a Remote I/O scanner, it does not need to be in the I/O tree at all.
 
Thanks all

thanks all,

i already replace the DH+/RIO module with the same firmware in my RSLogix5000, now i can see the slc500 in my RSLINX, i can't disable keying because that's my company regulation.

regards

Hanjaya
 

Similar Topics

Hi All; I am having a problem with RSLinx Classic seeing a DH+ network. We have a CLX processor with 2 (slot 5 and slot 6) 1756-DHRIO cards set up...
Replies
2
Views
3,833
How do I set up channel A on this module to communicate DH+ at 230.4k? Seems dip switch 1 set on 3 is invalid? Any help is appreciated. Kyle
Replies
4
Views
3,825
I'm trying to get a 1791r 8b8p to communicate with a 1756 DHRIO card. Both channel A and B on the DHRIO card are set to RIO. I have a 150 ohm...
Replies
3
Views
6,251
I have the above card series D in a 10 slot rack. Oddly enough every so often it seems to lose its connection to the main trunk on DH+. The...
Replies
2
Views
1,670
I am having a problem using a 1756DHRIO module to achieve remote access to a 1756-L55. We have a system with several PLC5s on a DH+ network...
Replies
3
Views
3,272
Back
Top Bottom