I am having a problem with RSLinx Classic seeing a DH+ network. We have a CLX processor with 2 (slot 5 and slot 6) 1756-DHRIO cards set up as a gateway between the DH+ networks and our Ethernet. One of the cards has a network connected to ch A and the second card has a network on Ch A and another one on Ch B. The DH+ networks all appear to be functioning ok, there has been no problems with our machines communicating but one of the networks (slot 6 Ch A) only shows the DHRIO node on RsWho, not the rest of the devices and I cannot connect to any of the PLCs by going through the ethernet connection. If I pull the card out of the processor and re-install then all of the devices show up on RsWho but only for a few secs before the red X's show up. The leds and message bar on the DHRIO card are showing everything as ok. This is a new problem, it wasn't happening last week and I can't see what might have changed.
I tried deleting the RSLinx driver and re-installing to no avail and I tried deleting the Harmony files-as Mickey says it can't hurt to try.
Right now this is only an inconvenience but I want to figure it out before it gets worse.
Thanks for any help you can give me.
Have you checked the configuration of the DH+ channels?
This is done from RSLinx - Right click / module configuration.
Mike_RH, thanks for the suggestion, I did check that and they were ok.
Found that I just needed to re-boot the processor, on the weekend the crew re-surfacing the floor used the PC outlet in the panel to run a grinder and killed the power. :mad: After the re-boot all is working ok.
Hello, I have a problem making a connection whit my PLC and the program factorytalk view studio. When i try to connect to my devices it shows...
10,657
We have a remove PLC rack that is being used to collect data from older equipment via a 1756-DHRIO module. This module occasionally faults out...
425
I am trying to send some datas from PLC-5 to control logix plc through 1756-DHRIO. When I go online to PLC-5, Message instruction gives error &...
3,381
:banghead: Remote I/O The occasional times i have had to deal with blue hose/PLC5 I/O addressing it always wrecks my head. Now i am working on...
3,294
Called to a site and am neck deep currently ;) running, but issues. Phase 2 completion has been running for almost 2 years no issues. Controller...
1,639