Hello.

I'm on my way to a plant to debug a problem they have. On one of Siemens analog in modules AI8 x 12 bit, 6ES7 331-7KF01-0AB0, There is the SF light on the top of the card lit.

I know of two scenarios that can cause this light to be lit.
1: The diagnosis for the card as enabled, but there is no sensor connected to the channel which is enabled.

2: The square dip switches, on the side of the card, which dip two channels (there are four of them) are not set according to the hardware configuration.

Do any of you know other things which can activate the SF light? I want to be prepared when I get to site, since they want to limit downtime as much as possible.

Thank you for any feedback.


brg
Andreas
 
The attaches picture is taken from Siemens Manuel (6ES7398-8FA10-8BA0)

All you need is there. In the PDF it is in 278th page (4-72)

Also after you tried everything mentioned. Check the backplane pins of the module and the backplane connector.

And likely the module could be broken down so you can need a new module...

AI_SF.jpg
 

Similar Topics

What is the best way to use relays to share a single analog input with several 4-20 mA 24VDC analog signals? Can you use timers to omit transient...
Replies
0
Views
5,346
So, we have one servovalve that is very critical to machine operation and idea is (or was) to detect if valve gets disconnected from analog output...
Replies
11
Views
2,903
Hello, We monitor the temperature of a pipe via a 4-20mA temperature transducer. This goes into DB135(Read Analog Inputs). The issue I have is the...
Replies
0
Views
625
I am setting up a new system and have an s7 1214 plc with an sm1231 4x AI (6ES71231-4HD32-0XB0). It is configured for 0-10v and has no faults in...
Replies
5
Views
1,143
Hey guys! I have come across an unique issue. Hoping that I can find some solution here. I want to replace an existing S7-1214 DC/DC/DC plc with...
Replies
15
Views
4,674
Back
Top Bottom