analog inputs ??

kumar

Guest
K
hey folks ...

i have a question regarding analog inputs in s7 200 plc's
what does A+ / A- / AR means ...and how can i connect them to the sensor i mean what kind of sensor ... i herd that there 2 wire type and three wire type ?? is that correct... and please give enough details about HOW TO CONNECT the sensor to the A+,A-,AR, inputs.

thanks in advance...
kumar.
 
Kumar,

the meaning of those connections is:
  • A+: analog input - positive side
  • A-: analog input - negative side
  • AR: analog input - resistor

The how to connect part is to be found in the "S7-200 Programmable Controller - System Manual" in chapters A.28 "Expansion Module EM231 Analog Input AI 3 x 12 Bits" and A.29 "Expansion Module EM235 Analog Combination AI 3 / AQ 1 x 12 Bits".

Kind regards,
 
hi jvdcande,
thank you for the reply ...

i have the manual that came along with the micro win document cd
but the part which i dont understands ...which of these A+ A- AR
give the PLC analog input the 0 to 10v signal,do you mean that the
A+ , A- are the power supply from the plc to the sensor ,and the AR is the sigle returned from the sensor to the plc input ?

can you please explain more jean ..... thank you in advance.

bebst regards .kumar.🍺
 
do you mean that the A+ , A- are the power supply from the plc to the sensor ,and the AR is the sigle returned from the sensor to the plc input ?
NO! The voltage output of the sensor has to be connected to both the A+ and the A- input as can be seen on the first figure in chapter A.28 (in my case figure A-27).

If you are using a current sensor, you have to connect the positive side of the sensor to both the resistor and the positive input of the module (shown are RC and C+) while the negative side of the sensor is to be connected to the negative input (here C-). In this way you generate a voltage across the resistor (current-to-voltage converter).

If you don't use a certain input you have to short the positive and the negative inputs (here B+ and B-) to avoid noise readings.

The internals of the module are shown in the fourth figure of that chapter (in my case figure A-30), which should clarify everything. The power supply of the sensors is not shown on these figures and has little or nothing to do with the PLC itself.

Kind regards,
 

Similar Topics

Hi all. I have 1793-IE4 (4)analog inputs modules in a 1794-ADN IOFlex DeviceNet Rack. I cannot find if I can I have access to individual channel...
Replies
1
Views
49
I am converting a SLC 500 to a Compact Logix. I plan on using a Compact Logix 5380 with conversion Kit. The problem is that the analog input cards...
Replies
1
Views
158
Hi there, I'm doing some extensive testing and commissioning with a slew of new Emerson PACSystems RX3i PLCs. It would be convenient to...
Replies
5
Views
137
Hello I need to message read the entire 16 channel raw analog inputs from a 1769-L33ER Compact Logic controller to another 1769-L33ER Compact...
Replies
8
Views
258
I have a SLC500 5/05 and we have an alarm setup to monitor the status of the Analog Inputs we have wired to a 1746-NI8. We are using 5 of the...
Replies
14
Views
2,842
Back
Top Bottom