Message Read entire Analog Inputs from CompactLogic to another CompactLogic PLC
Ones_Zeros
Feb 2014
at work
367
Hello
I need to message read the entire 16 channel raw analog inputs from a 1769-L33ER Compact Logic controller to another 1769-L33ER Compact Logic controller.
Can I do this with one MSG instruction? If this is possible how would I setup the MSG instruction source and destinations?
Thanks for helping
You can do it with a message instruction, produce/consumer, or if the analog is in a remote rack, you can possibly set the other processor up with the rack and IO in the IO configuration as listen only.
For message and produce/consume move the raw data into an array and just pass the entire array of values.
Thanks for the responses
Questions:
1. Since I'm only reading 16 channel raw analog data from a 1769-L33ER (PLC_1) into the remote 1769-L33ER (PLC_2) would I need to configure any consumed tags on PLC_1? Reason I'm asking is PLC_1 is online and I may not be able to take it off line to add the PLC settings in the Ethernet I/O tree.
2. PLC_1 - I would have to setup the Produced tag to send the analog data to PLC_2
3. PLC_1 - I would have to setup a DINT[16] to move all 16 analog inputs to Produced Tag DINT
4. PLC_2 - Would be my Consumed PLC and I would setup the same DINT[16] to accept the data from PLC_1
Maybe later when I can take PLC_1 offline then I can setup the consumed tags just incase I need to send data from PLC_2
Does this sound about right?
thanks again
One last question
If I'm unable to add the 1769-L33ER to the Ethernet I/O tree of PLC_2 into PLC_1
How would it know were to send the data to PLC_2? By Tagname
Just curious, if PLC_2 controller needs to be added maybe I can get a scheduled shutdown
thanks again for helping
One last question
Sorry I had sent the above response but after configuring the DINT[15] I can’t set the tag as a Produced tag while online with the PLC so I’ll have to have a temp SD and then I’ll configure the consumed tag on this plc even though it won’t be consuming any tags.
I did have a question
- can more that one consumed and produced tag be created in the plc?
- can I build a second consumed & produced tag and send some BOOL tags to the consumed PLC?
Thanks again
Yes, you can have multiple produce/consume. I usually create a UDT with both Reals and Dints in them. Use bits of Dints for boolean status passing.
We are going to pull 5-10 INT parameters out of 6 soft starts via explicit messaging in logix 5000. It's the only way we can read these over...
2,472
I have a 5069-L320ERS2 that has the scrolling LCD screen on the front. Is there any way for me to see what message is being displayed on that...
1,767
I would like to Read the CPU Usage % information like the Task Monitor tool provides from one ControlLogix to another via a CIP Message. Comms...
5,904
Hello Everyone, I am looking for some help on setting up a routing table on a DHRIO Module or perhaps the message configuration is wrong. I am...
3,003
Hello, I am trying to read a controllogix 32 bit array from a compactlogix using the MSG instruction and CIP Data Table Read message Type. So I...
4,716