Replace Communications in Panel View. What is that

bornwild

Member
Join Date
May 2010
Location
Riyadh
Posts
429
Hello folks.

I am just new to panelwview . I have to replace a bad panel view 1000 with a new one. I have the .mer file on my latop. While using the transfer utility there is a replace communication option. What does it mean? Replace communication? What communication. Also there is replace communication in panel view too?:confused:
 
Replace communicattions, is to replace the Default PV Comm Settings, with the settings incluided in the .mer file

So when you load the applications if you use Transfer utility, like i show in the image and you select run application at start up and replace communications, that message wouldnt appear anymore.

i hope this help to you

attachment.php


tranferutility.JPG
 
Just to elaborate a little more, the communications path that (which is the path that PanelView needs to take to get to the processor) is stored in two places. The PanelView and the runtime. The PanelView is always using the path that is stored in the terminal.

When you say yes to replace the communications, it means that you agree to apply the communications path that is stored in the runtime to the PanelView.
 
Thanks Gtr32 and dmroeder ,So if i dont check replace communications and download to mer file to panelview .Will PV not communicate with plc?
 
Thanks Gtr32 and dmroeder ,So if i dont check replace communications and download to mer file to panelview .Will PV not communicate with plc?

It depends.

In most cases, you will want to answer YES. if the comms settings in the PV+ don't match what you need, and you answer no, then it will not communicate.

You might answer NO if you used a common application in multiple locations and have already configured the communications before transferring the file.
 

Similar Topics

We have a Beckhoff CP6201 PC and an EK1100 module communicating with it via EtherCAT in one of our machines. Due to problems with the PC, I want...
Replies
0
Views
73
Panelview 2711-K5A8. Customer has 6 of these in service connected to SLC 504’s. One has a bad backlight and I need a solution to replace it...
Replies
11
Views
2,256
I’ve got some devices that are triggered by shorting pins to common. There is 24 volts on each pin and right now I am using a relay output card...
Replies
8
Views
2,565
I can't replace cpu S400 416-3XR05-0AB0 BY 416-3ER05-0AB0 in PCS7 Project when using replace object to keep the original configuration in the...
Replies
4
Views
1,503
How can I achieve the same functionality in Studio 5000? Image 001.png for the old RSLogix500 program Image 002.png for conversion to Studio...
Replies
6
Views
2,516
Back
Top Bottom