Intrinsically safe barrier

Kleinstick

Member
Join Date
Jun 2009
Location
Wisconsin
Posts
27
I was just reading another thread about trying to lock a door in a hazzard area, and it got me wondering. http://www.plctalk.net/qanda/showthread.php?t=58094

In my plant, we have hazzard areas and use Pepperl+Fuchs barriers. These were installed long before I came in here, and all I have ever done is add or replace them when the bosses say I should according to the wiring diagrams. I have no idea how they really work, what they actually do, or when they can be used.

Could one of these be used to control his door locks, and make them I.S. for the hazzard area?
 
They limit the amount of power available, so the spark is not capable of igniting anything. In my case, if the wires to our prox switches were sheared and shorted, we would avoid "spontanious relocation of personel and/or equipment." (My boss is fond of that one when talking about burners, but I think it applies here).

So the size of the load (I.S. side) is determined by the Imax? If (in the other thread) a system was available with a current draw within the Imax, he could have sent his signal thru a barrier and been ok?
 
Last edited:
Depending on the load of the locks it is possible. We use I.S. Barriers to fire solenoids all over our vessels.
So I agree it is a possible.
 
Could one of these be used to control his door locks, and make them I.S. for the hazzard area?

Most likely not. Just putting a barrier in the circuit does not satisfy the requirements. The actual device must be identified as I.S. by the manufacture, unless it is a 'simple' device. Simple devices include RTD's LED lights, potentiometers, etc. They do not produce heat, sparks, arcs, nor store energy.

mjaye65: Your solenoids would have to be I.S. rated if they are in a Class I Division 1 Area. I have used hundreds of that type.
 
Most likely not. Just putting a barrier in the circuit does not satisfy the requirements. The actual device must be identified as I.S. by the manufacture, unless it is a 'simple' device. Simple devices include RTD's LED lights, potentiometers, etc. They do not produce heat, sparks, arcs, nor store energy.

mjaye65: Your solenoids would have to be I.S. rated if they are in a Class I Division 1 Area. I have used hundreds of that type.


So, I can only use an IS barrier on a device that is already certified to be IS, and does not need a barrier? I know I am the newbie here but my "you made that up" detector is pinging.
 
If I were trying to 'lock a door' in a haz. area, I'd remove all the electrical stuff, and use a non-electrical system, like a captive key exchange lock, or something similar.
 
So, I can only use an IS barrier on a device that is already certified to be IS, and does not need a barrier? I know I am the newbie here but my "you made that up" detector is pinging.

I didn't say that. And I'm not trying to argue. But rather be very explicit. A device that is I.S. rated will need an I.S. circuit. You could use a Barrier, Isolator or other means of protection. If fact, I don't think the Code actually mentions Barriers or Isolators.

I didn't say Certified, but rather Identified. A Barrier is one type of protection technique. The device itself is documented by its manufacture how to be used in an I.S. circuit.

Now all this talk is about "Hazardous Areas", but yet the actual classification type of the area has not been specified. For each type there are different protection type minimums that are required.

If you would like to view the NEC code book online for free, register at nfpa.org and see page http://www.nfpa.org/onlinepreview/online_preview_document.asp?id=7008SB

You may also with to read the messages at http://forums.mikeholt.com/forumdisplay.php?f=73 about Hazardous Areas
 
Properly installing an I.S. circuit is not easy, there are many details that must be met and maintained per NEC Article 504. The benefit, though, is a large savings in electrical circuit installations in Div 1 locations.

Generally, for a Class 1, Div 1 hazardous area you will see electrical systems installed using explosionproof wiring methods or I.S. wiring methods, or both.

Barriers are necessary for a properly installed I.S. circuit, but are also sometimes used as supplemental protection for explosionproof installations (many times because the intention was to have I.S. circuits, but the installations fell short of meeting all requirements during construction so the can't be true I.S. circuits..)

Also relating to barriers, there are different barriers used depending on the circuit - a discrete output, a discrete input, an analog input, and a 3-wire RTD for example would use different barriers with different diode configurations inside of them and with different specs.
 

Similar Topics

OK I just got dropped in another somewhat odd job. I have to do have safety door switches E-stops in a classified area Class 1 DIV 1. The...
Replies
19
Views
6,859
I need to provide a USB connection for data transfer to a USB Thumb Drive on a purged panel. Are there Safety Barriers available for USB connections?
Replies
4
Views
6,811
It is my understanding that an LED is considered a simple device, making its use fairly simple in an IS application. However I am running into a...
Replies
22
Views
5,879
I have a customer that is requesting an Intrinsically Safe HMI. I can't say that I've ever heard of an Intrinsically Safe HMI. Anybody here have...
Replies
17
Views
4,559
Hey, does anyone have any experience with such a device? I need to have an RFID reader set up in one of the paint booths we have. Thanks! -PreLC
Replies
3
Views
1,567
Back
Top Bottom