Intrinsically Safe HMI for Zone 2, IIA/IIB, T3
John Marston
Apr 2015
Chuparosa
54
I have a customer that is requesting an Intrinsically Safe HMI. I can't say that I've ever heard of an Intrinsically Safe HMI. Anybody here have any experiences with one they like?
in order to make an hmi safe, you must purge / pressurize the enclosure to acceptable levels. all ab terminals that i know of cannot be purged / pressurized because the display will bust under pressure. this goes for all other displays that i am aware of. Maple Systems used to make a computer hmi system that would meet your requirements, but that was years ago for 10-20k depending on your requirements and screen size.
james
Yeah, I typically purge the HMIs I use but this customer is wanting one that has a protection method of Intrinsically Safe. Siemens may have one but making sense of their terrible website is usually more trouble than its worth.
I came across the possiblity of Siemens maybe having one as well but like you I cannot stand their web site to look into it much more. Also I am not familiar with non NEC classifications, maybe an IS Tablet would be better suited for the customer?
Snyd1,
2008 version - see NEC 70, section 505
looking at these specs, i doubt the customer will ever get what he wants, too many chemicals, gases.
the companies that i worked for since 2004 has provided me the code books.
james
Try the configurator
https://new.siemens.com/global/en/products/automation/topic-areas/tia/tia-selection-tool.html
Click start tia selection cloud
Select New Device > Industrial PC > Monitor & Thin Client > Pop up click select device series > Simatic HMI Ex tab.....
Then click through each one to see what Ex standards they comply to
Snyd1,
james
Thanks,
Never had to delv down into the groups before. Glad I do not have to deal with that stuff, not sure I would ever sleep again.
I'll throw in Bartec and Pepperl-Fuchs for HMI and Thin clients respectively.
When the customer says intrinsically safe, what's his understanding of it? I've seen chemists requesting Exd devices to be made intrinsically safe with a barrier which is absolute nonsense and a likely non-compliance.
I can't remember of one HMI device that is powered by an intrinsically safe circuit as most barriers can't output full amps. Generally the device itself is internally intrinsically safe (the marking features ia, ib or ic within square brackets), but it'll have an additional marking (either d, e or n).
Looking at your requirements though, you can find a bunch of Ex n marked devices that comply with this.
I think the important bit is understanding where this requirement of the intrinsically safe comes from and why as you may well be able to successfully argue that it's either not possible or far more expensive than what they'd be willing to pay.
After all, it's a Zone 2, IIB T3... it's not Zone 1, IIC, T6 so there's plenty of leeway to deliver something fit for purpose without overengineering based on someone's ignorance.
Hi, I have a Class 1 Div 2 HMI and would like to supply the 24 Vdc power through an isolation barrier. I cannot seem to find any barriers out...
19
4,144
Hello All, We have a HMI ,a Mecury 2e Intrinsically Safe HMI. Does anyone know what is required to 1: Download an existing backup to a HMI or 2...
2,638
It is my understanding that an LED is considered a simple device, making its use fairly simple in an IS application. However I am running into a...
22
5,887
Hey, does anyone have any experience with such a device? I need to have an RFID reader set up in one of the paint booths we have. Thanks! -PreLC
1,581
I had a chat today with a contractor and he notified me that Rockwell will stop producing the Flex Ex IO modules from December 31st. The ones we...
1,657