Im using FT view Machine, I have slc 500 5/01 I cant see plc with FT. I can program and change program with rslinx classic from laptop. Im trying to simulate my program.
 
The SLC-5/01 controllers have only a Data Highway 485 (DH485) network port, so you must be using some kind of DH485 driver in RSLinx Classic.

What exact physical interface are you using between your PC and the SLC-5/01 controller ?

FactoryTalk View can use RSLinx Classic as an OPC Server, but it is more common for it to use its built-in data provider, called RSLinx Enterprise.

RSLinx Enterprise and RSLinx Classic don't share the same physical hardware, so you probably have a physical resource conflict, like a serial port conflict.

When I have to use serial interfaces to SLC-5/0x controllers along with FactoryTalk View, I usually use two: one for RSLinx Classic and one for RSLinx Enterprise.
 
Im using 1746 UIC adapter. I try to use the rslinx enterprise but just keeps brousing, wont find it. How would I use two?
 
You may want to dig a little deeper, but there are some subtle differences in the way that the 5/01, 02 respond to Dh485 messages as compared to the 5/03 and newer.

SURELY A/B handles this correctly with the new UIC (I don't yet have one)?

Ken would know (or have access to details) for sure if anyone does....he's the A/B comms guru, hands down...
 
If you have an OPC-capable version of RSLinx Classic (not Lite) you must create an OPC Topic that points to the controller first.

Then, in FactoryTalk View Studio, you right-click in the project and select "Add OPC Data Server". This will let you select the RSLinx Classic OPC servers as data sources instead of RSLinx Enterprise.

I do not recommend this method to an inexperienced user, because switching back to RSLinx Enterprise (so that your application will run on a PV+ terminal) can be tricky.
 

Similar Topics

I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
Replies
10
Views
258
can the slc500 5/05 send a email and text over Ethernet ?
Replies
3
Views
185
Hello, did anybody know, if there exist an converting cable like the1492-CM1746-M01 (for an 1746-IB16 to an 5069-IB16), for an 1746-HSCE to an...
Replies
3
Views
389
Customer is buying several spare 504 CPU's to have one handy when there's an issue with the ones in operation. Having them on the shelf for years...
Replies
15
Views
2,835
You have to go offline to create the 'Trend' but do you have to download the program to go back Online with the Trend ?
Replies
0
Views
344
Back
Top Bottom