Unsued Output Flickering

seaston_65

Member
Join Date
Nov 2008
Location
Ontario
Posts
47
I have a machine here running a MicroLogix 1400.
There is an "unused" Output (O:0/2) that I wanted to use for something but I've noticed that it seems to be used.
It looks like that O:0/2 is actually set up to Pulse whenever O:0/4 is ON.
If I cross reference O:0/2 it's not is use, and I've check the entire Output word and nothing in the ladder logic is telling it to pulse, but if I monitor O:0/2 online I can see it turning ON and OFF.

Is there somewhere that you can configure an output to do this or could some other kind of issue here?

Thanks
-Shawn
 
Check your function file configuration. Look to see if either a PTOX or a PWMX function file is using that output. PTOX and PWMX function files have three elements each. They can be configured to use outputs 2, 3, or 4. Look at all six elements and see if you see a value of 2 for the .OUT parameter under any of them. If you do see a 2 then output O:0/2 is being controlled by that function file.
 
Last edited:
Check your function file configuration. Look to see if either a PTOX or a PWMX function file is using that output. PTOX and PWMX function files have three elements each. They can be configured to use outputs 2, 3, or 4. Look at all six elements and see if you see a value of 2 for the .OUT parameter under any of them. If you do see a 2 then output O:0/2 is being controlled by that function file.


It's used under PTOX
Thanks for pointing me in the right direction. I knew that an output could be setup to do that, I just didn't know where to configure it.

Thanks for all the help guys.
 

Similar Topics

Hey all, I am starting a new project for a customer and I am adding in solenoid valves. Once added, I noticed there was a lack of an Output...
Replies
0
Views
68
Hi, The hardware is: Click Plc model # CO-O1DD1-O HMI model # S3ML-R magnetic-inductive flow meter model # FMM100-1001. I will set the flow meter...
Replies
4
Views
136
Hi, I am using AB 5069-L306ERS2 CPU. My system should achieve SIL-2. I have safety door switches connected to AB 5069-IB8S module, and I want to...
Replies
1
Views
110
Hello! Hope you are great. I need to make a change in a PLC with ladder logic. I will mount a analog valve and I need to control it in ramp up...
Replies
7
Views
319
I have a 170AAO92100 card that I am interested in using as a 10 volt output. Is there setup that I have to do in order to change output or simply...
Replies
0
Views
86
Back
Top Bottom