SIEMENS: DP Slave not avaiable and OB85

Indiaum

Member
Join Date
Jan 2010
Location
Brasil, Minas Gerais
Posts
54
Hi guys!

First, sorry about my english and thank you for your attention.

In my rack i have a CP 443-5 Ext. (Profibus Module) and in its bus, Softstarters and Simocodes. My problem is, if one of them gets unavaible for any reason my CPU goes to STOP MODE. In diagnosis i read that the reason is the lack of OB85, so i add it to my project. Now my CPU keeps running with EXTF LED lit. CP 443-5 lights up EXTF and BUSF blinks.

I can`t stop my plant just because a dp node of that type became unavailable.Is this an acceptable method of doing so?

Thank you.
 
Last edited:
I found out a similiar solution and it looks much more reliable. But still, not sure if it is appropriate.
In HW Config, under Options, theres "Report System Error". This will generate all OBs and SFCs necessary to handle rack fault, module fault and others, with the option to choose the behavior of the CPU in case of any of this faults...and other functions that i didn't figure out yet what they do xD.

Sorry about my english, and thank you for your attention.
 

Similar Topics

if we need to take back up of Siemens CPU(s7300 /s7400) with non siemens slave profibus nodes without their gsd files and when we restore it in...
Replies
0
Views
86
What is the best practice way to make remote procedure calls from a Siemens s7-1200 PLC to a C# app running on a PC (app is directly controlling...
Replies
1
Views
1,225
I'm putting together a system with a Redundant S7-1500 CPU and 2 Comfort HMI’s on an MRP ring. The HMI’s will be doing the same job and only one...
Replies
3
Views
1,745
Dose anyone have experience with Beckhoff FC3121 profibus master PCIe card connected to Siemens CP342-5 as a profibus slave? The data retrieved...
Replies
17
Views
4,859
Hello Guys, I have s7-315-2 PN/DP with integrated DP. I have no CP module. PLC should be DP master. ON other side there is basler device DECS250...
Replies
6
Views
3,506
Back
Top Bottom