hi am rohit working on compact logix L32E i have to work on modbus but i have not experience on modbus protocol please any body guide me how to develop modbus list i have used AIC card of Allen bradlley for modbus protocol send any pdf that can help me please please it to urgent please
 
You should tell us your problem. What are you trying to get to talk? 485, 232, 422, or Ethernet?
 
Please try to post using formal English sentences. It will help the rest of the Forum read your posts more easily, and result in better advice for you.

Modbus RTU protocol can be implemented in the CompactLogix controllers using standalone gateway devices, backplane modules, or using ladder logic and the serial port of the controller.

The example routines for using the serial port are described in this Application Note:

http://literature.rockwellautomation.com/idc/groups/literature/documents/ap/cig-ap129_-en-p.pdf

The revision notes for the example routines are in the Knowledgebase:

http://rockwellautomation.custhelp.com/app/answers/detail/a_id/55213

And the example routines themselves are installed along with RSLogix 5000 in the Sample Programs directory, usually in a folder like "C:\RSLogix 5000\Projects\Samples\ENU\v18\Rockwell Automation"

A copy of the updated RSLogix 5000 v18 example program is also in the Knowledgebase, but requires a TechConnect contract:

http://rockwellautomation.custhelp.com/app/answers/detail/a_id/42662

All of the example code is usable and functional but it is not suitable for a user with no Modbus experience.

If you are unfamiliar with Modbus I very strongly recommend that you use an external gateway device from Prosoft or HMS Fieldbus, or a chassis-mounted interface like the Prosoft 1769-MCM.
 
Great summary, Ken. That is a 5 star post.

3089jjn.jpg


It should be a 'tutorial'.
 

Similar Topics

Hi all, I'm really new to this. I need to export the Modbus register mapping from a Modicon M580 through Control Expert for the registers that...
Replies
4
Views
981
Could someone help me understand how the modbus mapping is handled for the MotionWorks IEC software? I have an existing application where I have...
Replies
0
Views
1,130
I've got a project which requires some Logix integration to a Danfoss device. It is the controls part of an Integrated Technologic Sensorless...
Replies
10
Views
2,957
Dear all, In CCW modbus Adress mapping where each adress is configured in modbus mapping option.For example I will be mapping some memory bit or...
Replies
1
Views
2,142
Got a 2080-LC30-24QWB with 2080-SERIALISOL card hooked up to a Modbus slave device. MSG_MODBUS instructions are working fine. I am trying to set...
Replies
1
Views
3,738
Back
Top Bottom