Hi all
I want to control the speed of VLT 2800 frequency invertor "from DANFOSS" using S7 siemens PLC via profibus cable. i want to do this application using three sensors for speed controlling.I already connect my components and finished the hardware configuration but i need a ladder diagram for my application.
Thanks
 
S7 <-> Drive

Hello,

Useful link:
http://www.proces-data.dk/5C/00602K4MVH/FCGK6-01/Description_ENG.htm

Did you ever wrote a communication for a device on profibus ?

What you need to do:
- Install GSD file.
- Change the communication parameters of the drive (speed source and commands source).
- In the hardware config of the PLC => choose a PPO type or user defined, most easy PPO type is PPO3.
- If you use PPO3 then you have a Controlword, a setpoint frequency, a Statusword and a actual frequency word.
- Then you need to know what to send to the control word and scale you PLC setpoint to the setpoint frequency of the drive. Mostly this is 4000 Hex, 16384 dec. If you work with the frequency 0-50Hz in the PLC, then you must rescale like this: (PLC_VALUE/50.0) x 16384

Regards,
Gerry

Hi all
I want to control the speed of VLT 2800 frequency invertor "from DANFOSS" using S7 siemens PLC via profibus cable. i want to do this application using three sensors for speed controlling.I already connect my components and finished the hardware configuration but i need a ladder diagram for my application.
Thanks
 
Combo

HI,I HAVING PROBLEM WITH DUNFOSS DRIVER VLT2800 (ALARM) ERROR 15
I CHECK IN THE MANUAL ,ITS SAID THAT SMPS FAULTY ,I DISMANTELLING THE DRIVER AND CHECK THE CAPACITOR IS HIGH VALUE 220uF/35V ,WHEN I MEASURE WITH LCR TESTER ITS SHOWING 229uf/35v there have 4psc so i replace all of the 4psc and see,the ALARM STILL APPEARS ,AND I CANNOT RESET ...... CAN ANY ONE TELL ME WHERE WILL BE THE FAULT IN THE DRIVER?

THANK YOU
 

Similar Topics

Hi All, I am facing one issue with the SEW MDX61B drive. Issue- I want to run a conveyor with this drive in two directions but it runs in...
Replies
0
Views
353
Hello, I'm trying to configure Profibus communications between a CPU1214c by module cm1243-5 and a Parker 590 DC drive. in tia poral software, hex...
Replies
0
Views
1,128
Dear Sir, I have a healthy profibus communication between SIEMENS PLC S7 400 and Allen Bradley drive PF700 using 20-comm-p profibus dp module...
Replies
3
Views
2,843
Experts! Need Help In My application i have Siemens CPU 316 WITH APPROX 28 PROFIBUS NODES (including Simovert Master Drive -14N.o.s & IM153 &...
Replies
5
Views
4,911
Dear superiors, When i try to communicate Yasakawa A1000 AC Drive and simense s7-300 plc via profibus the drive shows error bb on its display...
Replies
16
Views
6,928
Back
Top Bottom