Valve is Atos DLK ZOR-TE-140-L73
This is a direct drive proportional with OBE Operating a 430mm (17") cylinder at 290 bar (4200 psi)
I have tried three different valves, including two brand new valves and all behave the same way.
When I slew command to the valve with the hydraulic pump off the valve spool position feedback follows the command very tightly, both for positive and negative command.
When I slew command with the pump turned ON then the valve spool tracks command up to about 25%. Then the spool stays at ~25% even if command increases up to 100%. If command decreases then spool tracks just fine below 25%.
If I put command anywhere between 25% and about 60% and turn the pumps off then the spool position immediately shifts to match command. If I turn the pumps back on spool position drops back to 25%.
If I put command anywhere above 65% and turn the pumps off spool position will them move to match command and when I turn the pumps back on it will remain there and track command up and down just fine all the way to 100%.
If I start at 100% command and 100% spool position and turn the pumps on and slew command to 0 then the spool will track command almost perfectly going down but will not track going back up.
This condition holds for both positive and negative valve commands.
Its almost like the valve doesn't have enough power to move the spool through the mid-range but I've checked the power supply and there is no voltage drop off.
I've checked the controller analog output to the valve and it is fine, same with its analog input for the position feedback.
I have several identical systems and none of the others behave this way.
Any ideas?
This is a direct drive proportional with OBE Operating a 430mm (17") cylinder at 290 bar (4200 psi)
I have tried three different valves, including two brand new valves and all behave the same way.
When I slew command to the valve with the hydraulic pump off the valve spool position feedback follows the command very tightly, both for positive and negative command.
When I slew command with the pump turned ON then the valve spool tracks command up to about 25%. Then the spool stays at ~25% even if command increases up to 100%. If command decreases then spool tracks just fine below 25%.
If I put command anywhere between 25% and about 60% and turn the pumps off then the spool position immediately shifts to match command. If I turn the pumps back on spool position drops back to 25%.
If I put command anywhere above 65% and turn the pumps off spool position will them move to match command and when I turn the pumps back on it will remain there and track command up and down just fine all the way to 100%.
If I start at 100% command and 100% spool position and turn the pumps on and slew command to 0 then the spool will track command almost perfectly going down but will not track going back up.
This condition holds for both positive and negative valve commands.
Its almost like the valve doesn't have enough power to move the spool through the mid-range but I've checked the power supply and there is no voltage drop off.
I've checked the controller analog output to the valve and it is fine, same with its analog input for the position feedback.
I have several identical systems and none of the others behave this way.
Any ideas?