Hi.
I am playing with an MSS system and trying to get a project working, but Step 7 won't let me download FB980 (the diagnostic block) to the 314c-2DP CPU.

It returns the error:
Download (294:6)
Unable to copy the block FB980

It says the same for DB980 also.

The CPU is in stop, the FB (1952 bytes) and DB (4142 bytes) numbers and sizes are all within the max limit for the CPU (FB up to 1024 block, permitted no's 0-7999, max size 64KB).

But I can download to the simulator fine - no issues...

Has anyone experience any issues like this and got a work-around?

Cheers.
 
The PLC memory may be full. Delete FB980 from the plc and then download. If successful, repeat for DB980.
 
When the error message pops up, there will be a button to get more expanded info as to why it will not download.
As LD says, it is probably a case of the load memory being full.
 
Thanks for the reply. The CPU memory is empty, I did a overall reset prior to downloading the FB...
When I click the Details tab, I get these messages:

Download (294:6) - Unable to copy the block OB1.
Download (33:53888) - (D280) Error compiling block in S7-300 CPU.
 
Isn't there limits for FC/FB numbers with some S7 Cpu's?

Try changing the FB number much lower.
 
You get these type of messages if you try to download blocks that contain timers/counters/flags which are out of range for the CPU. Could this be the problem?
 
The limits for a 314 CPU are:
FB
Quantity - 1024
Permitted Number - 0 - 7999
Max Size - 64KB

FC
Quantity - 1024
Permitted Number - 0 - 7999
Max Size - 64KB

DB
Quantity - 1024
Permitted Number - 1 - 16000
Max Size - 64KB

-- From the Siemens Instruction list S7-300 CPUs and ET 200 CPUs manual --
 
This is all OB1 contains
v6logi.jpg
 
Yes there are limits.
It is a deficiency that STEP7 doesnt check FC, FB and DB numbers, as well as Merkers and Timers against what the CPU actually support.

Stupid question: What size is the installed MMC card ?
Check also the load and work memory in the online CPU properties.
 

Similar Topics

I have never had the pleasure of working with a "Thermistor" until now and have a question. The Thermistor is a 10KOhm 4-20mA 2-wire device and I...
Replies
2
Views
45
Hello, I have a CPU 317-2DP Firmware Version V2.1.8. In TIA Portal only V2.6 is available, and there is no option to upgrade FW. Then I open it...
Replies
9
Views
168
HI everyone, i am new to Siemens plc programming and i am in need of some help. yesterday we had an S7-1200 CPU 1214C fail to turn on an output to...
Replies
12
Views
391
Hi PLC people, think about this scenario: The PLC is somehow connected to the same network with the facilities` network. Then someone connects to...
Replies
2
Views
119
Hello everyone, I've had this issue for the last 2 days where I try to assign the profisafe address to an IO block (6ES7 146-6FF00-0AB0) but when...
Replies
5
Views
169
Back
Top Bottom