Siemens MSS FB980 & 314C-2DP - Can't download

The properties of OB1 and FB980 are:
OB1 -
Load - 180 bytes
Working - 110 bytes

FB980 -
Load - 2904 bytes
Working - 1952 bytes
 
This is a very old CPU. The specs you listed are probably from the latest CPU.
Max datablock no is 511. (for 314-6CF02-0AB0 which is a bit newer but not latest version)

Where did you find this information?
I was looking for ages and only came across was in the manual, 6ES7398-8FA10-8BA0
 
I have copies of most Siemens manuals.
The oldest S7-300 spec I have listed the data for 6ES7314-6CF02-0AB0.
edit: It is possible that FC, FB and DB numbers are even more limited in your 6ES7314-6CF01-0AB0 .
edit: The magic maximum numbers you can try are 255, 511, 1023, 2047 and 4095.
 
Last edited:
right click your CPU inside the hardware editor and you get the following options;

Product support information
FAQ's
Manuals

hardware.jpg
 
I was wondering what you get for the 314 ? You can only download FC0 to FC7999 to the 317 I've shown in the previous posts.
 
Last edited:
Thanks guys, I tried downloading the project (the OB and FB) to a 317-2DP and everything downloaded ok.
So based on what you have said it seems to be down to the firmware version running on the CPU.

We have a load of CPUs around, how would be the best way to quickly find out what restrictions we have for each of the CPUs?

Also, did the manual tell you specifically what the spec was for the 6CF02?
 
If you use STLs advice, select "Technical Support info", and then the "Technical/CAx data" tab. It will give you the exact information:

DB1-DB511
FC0-FC511
FB0-FC511
 
You can determine the limit by running the following code in the plc and then monitoring MW100. Make sure there are no other blocks in the plc though.....
 

Similar Topics

Hi, I'm setting up a modbus master on an S7-300. It seems to work in OB1 but not when I use it in OB35. Does anyone have any ideas why? Could...
Replies
10
Views
86
The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
12
Views
322
Hello I have a s7-1200 and I would like to read the tags present in this controller with my controllogix controller. The two controllers don't use...
Replies
5
Views
167
Hi need help why this “failure 5 emergency stop “ appears at every startup in the morning ? Have to shut off main switch at least 10 times on...
Replies
19
Views
317
i have two plc 1. s7-1212dc/dc/dc ip; 192.168.0.1 2. s7-1500 1513-1pn ip; 192.168.3.2 i need to get data from plc1 to plc2. any idea how to do...
Replies
5
Views
128
Back
Top Bottom