why PV not showup in Micrologix PID setup screen?

wilsonzhu

Member
Join Date
Jan 2008
Location
vancouver
Posts
278
HI,

I am using Emu 500 to test Micrologix 1100 program, The PID setup screen don't show up PV value which address is N17:36(range is from 0-16383). why? Thanks,
 
Let me be a little less abrupt.

I set up a MicroLogix 1100 program and entered it with similar addressing for the PID instruction and saw that the value in N17:36 doesn't show up in the PID configuration dialog offline in RSLogix 500, or online when you run the program in RSEmulate 500.

I assume that this is because the PID instruction is not executing, as the RSLogix 500 Emulator does not support the PID instruction.

Specifically, as cited by RA Knowledgebase document 55723, "The software does not attempt to execute the PID instruction or change any of the PID control bits or words."

If you were to run this program in a physical MicroLogix 1100 controller, I am confident that the PV value would appear correctly.
 
Last edited:
Thanks very much!

Let me be a little less abrupt.


I set up a MicroLogix 1100 program and entered it with similar addressing for the PID instruction and saw that the value in N17:36 doesn't show up in the PID configuration dialog offline in RSLogix 500, or online when you run the program in RSEmulate 500.

I assume that this is because the PID instruction is not executing, as the RSLogix 500 Emulator does not support the PID instruction.

Specifically, as cited by RA Knowledgebase document 55723, "The software does not attempt to execute the PID instruction or change any of the PID control bits or words."

If you were to run this program in a physical MicroLogix 1100 controller, I am confident that the PV value would appear correctly.
 
Let me be a little less abrupt.

I set up a MicroLogix 1100 program and entered it with similar addressing for the PID instruction and saw that the value in N17:36 doesn't show up in the PID configuration dialog offline in RSLogix 500, or online when you run the program in RSEmulate 500.

I assume that this is because the PID instruction is not executing, as the RSLogix 500 Emulator does not support the PID instruction.

Specifically, as cited by RA Knowledgebase document 55723, "The software does not attempt to execute the PID instruction or change any of the PID control bits or words."

If you were to run this program in a physical MicroLogix 1100 controller, I am confident that the PV value would appear correctly.

Sorry for hijacking, but I'm running a PID on a ML1100 and have the same problem. In my case, the PV is stored in N7:6, but it doesn't show up in the PID setup screen. I've been researching this all day to no avail.
 

Similar Topics

Hey all, first time poster here. I am wondering if anyone has tried using a Keyence SR-X300 barcode scanner to a Micrologix 1400. Keyence sent...
Replies
0
Views
28
I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
82
I'm using a SLC typed write from the ControlLogix5572 to the MicroLogix 1400, with path: 2, (MicroLogix IP). The ControlLogix equipment has a...
Replies
0
Views
89
"Hello! Good day! Excuse me, I have a question regarding the 1761-NET-ENI. RSLinx has already detected it but it's not connecting to the PLC...
Replies
4
Views
129
Hi, I cannot find the DLCA1764.EXE utilty software for data retrieving. Can someone share the link to download this software. Thanks!
Replies
4
Views
119
Back
Top Bottom